MrWong

Hello All,

I have decided to write a post whether a old wok range cooker requires a gas interlock system? The wok range is well over 10 years old and in a very good condition. The gas engineer came over and inspected the wok and said it has failed due to no gas interlock system and fail safe device. I was told due to new regulations that the wok system needs to install these safety devices and was quoted at a ball park fugure of £1,500.00. In other hand, speaking to other people who had similar experience with me and I was told that if it was a old wok range then it does not require these safety devices. I am confused??? Any suggestions?:90:

Kind Regards

Wong
 
Yes it does.

There's a gas technical bulletin which I'm afraid you won't have access to that refers to this - TB140.

A gas detection system needs to be interlocked with your supply and extract fans. This would prevent the gas being turned on without them running.

And with the age of your appliance gas proving would need to be incorporated too. This tests the pipework and appliance downstream of the safety valve.

You've been advised correctly.

Pay him well Mr Wong, he's probably saved your life and your business.
 
Last edited by a moderator:
If he is talking about an interlock sytem then im guessing this is a commercial application.
With domestic cooking appliances if they are of a certain age then they may not need a flame safety device but im pretty sure thats out of the window with commercial catering. That could be where your friends confusion has come from.

Talk to your insurance company too, they will likely have something to say about not covering you if you don't comply or do not have an interlock in a comercial catering application

In the grand scheme of things that isn't a large price tag, it also removes human error which could leave your establishment as a hole in the ground, litterelly.

No brainer.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Many thanks for the reply @Timmy D thats a...
Replies
5
Views
982
Just browsing the threads and this one here //...
Replies
0
Views
1K
And to make it even clearer, the fact that the...
Replies
6
Views
3K
Is the gas pipe magnetic?
Replies
3
Views
3K
Back
Top