I C.H. system with a combi boiler. 4 rads on 1st floor,1 in the attic and 2 on ground floor heat up perfectly but 1 of 3 rads on the ground floor does not heat up. It gets warm across the upper 1/3 part after at least about an hour. 22mm return and flow pipes feed all of the mentioned radiators via 22mm x 10mm (metallic bronze) manifolds on first and ground floor. Hot water from the boiler gets to one side of the rad but does not flow back to the return pipe through it. I have done the following work to resolve the problem without any joy.
1. TRV & lockshield valves checked - found functional not seized,
2. suspected blockage in the radiator, return pipe to the manifold - rad
flushed and pipe checked but there was neither blockage in the rad nor
any sign of restriction in either pipe or in manifold - rad still cold,
3. air lock in the pipes and the the rad in question checked,
4. pump is checked, the whole system balanced, all of the upper floors
rads turned off - pump found running fine and no difference observed on the ground floor rads,
5. turned off all of the rads including ground floors except the one in
the question - No Joy! A mystery.
6. coupled TRV and lockshield valves using a 15mm pipe - Hot water
from flow side flows to the manifold at the return pipe.
I am planning to change replace 22mm x 10mm manifold to 22mm x 15mm manifold. Boiler is situated in the kitchen on ground floor. The above mentioned mysterious rad is in the living room i.e. nearest to the boiler. It is very mysterious problem. Any advice / suggestion from fellow forum members would be appreciated.
1. TRV & lockshield valves checked - found functional not seized,
2. suspected blockage in the radiator, return pipe to the manifold - rad
flushed and pipe checked but there was neither blockage in the rad nor
any sign of restriction in either pipe or in manifold - rad still cold,
3. air lock in the pipes and the the rad in question checked,
4. pump is checked, the whole system balanced, all of the upper floors
rads turned off - pump found running fine and no difference observed on the ground floor rads,
5. turned off all of the rads including ground floors except the one in
the question - No Joy! A mystery.
6. coupled TRV and lockshield valves using a 15mm pipe - Hot water
from flow side flows to the manifold at the return pipe.
I am planning to change replace 22mm x 10mm manifold to 22mm x 15mm manifold. Boiler is situated in the kitchen on ground floor. The above mentioned mysterious rad is in the living room i.e. nearest to the boiler. It is very mysterious problem. Any advice / suggestion from fellow forum members would be appreciated.