buckley plumb
fitted a betacom 28a about 5 months ago and got called back to it today due to poor ho****er - checked at taps only 39degrees with tap on full flow or low flow . water temp set at 60 - 14 degres across plate - flow 73 rtn 56 on boiler . checked fan target and actual values which were ok . inlet pressure 20mb on full . only thing i could see was the burner seemed to hunt up and down . called glowworm out under warranty they are coming tomorrow . asked customer to get engineer to write down what fault was . i was thinking thermistor due to only 73 on flow or fan