buckley plumb

fitted a betacom 28a about 5 months ago and got called back to it today due to poor ho****er - checked at taps only 39degrees with tap on full flow or low flow . water temp set at 60 - 14 degres across plate - flow 73 rtn 56 on boiler . checked fan target and actual values which were ok . inlet pressure 20mb on full . only thing i could see was the burner seemed to hunt up and down . called glowworm out under warranty they are coming tomorrow . asked customer to get engineer to write down what fault was . i was thinking thermistor due to only 73 on flow or fan
 
engineer rang me to let me know the problem - was the shower mixer valve letting cold into the hot causing the boiler to fluctuate burner all over the place .he turned the cold supply to the boiler off and turned the hot tap on - there would be a pulsed flow as mentioned from the shower mixer. you learn something new every day
 
Status
Not open for further replies.

Similar plumbing topics

Finally (I hope) got to the bottom of this...
2 3
Replies
55
Views
5K
Hello All- (Usual caveats apply: I am the...
Replies
0
Views
205
    • Like
From this post, I think you’ve got a good...
2
Replies
47
Views
6K
R
  • Locked
Sorry fella, much as we'd love to help you we...
Replies
1
Views
1K
Dotty
D
  • Locked
hello beesley the heat hex is as we speak is...
Replies
4
Views
4K
Back
Top