One pipe system special rad valves | UK Plumbers Forums | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss One pipe system special rad valves in the UK Plumbers Forums area at Plumbers Forums

Matt0029

Gas Engineer
Messages
1,177
Are rad valves used on a one pipe system usually specialist less flow restrictive to normal valves? Possibly have a bathroom rad to swap for a towel rad. On one. Also can a modern towel rad. Be too flow restrictive for a one pipe system?
 
Tbh lockshield valves only don’t tend to fit trvs
 
Should work if it's s standard towel rad. Avoid any which require the flow on a specific connection. As for valves standard valves will work but avoid things like Drayton trv as the have those small holes which may be yo restrictive. I'd use standard straight lockshields out of the floor. Sweep tees can be brought for around 5-6 quid.
 
Should work if it's s standard towel rad. Avoid any which require the flow on a specific connection. As for valves standard valves will work but avoid things like Drayton trv as the have those small holes which may be yo restrictive. I'd use standard straight lockshields out of the floor. Sweep tees can be brought for around 5-6 quid.
Thanks there also interested in a vertical collum radiator around 400mm wide 1000 to 1500mm heigh. Any chance of this working?
 
Or is there a reason one like this wouldn't work on a one pipe system
 

Attachments

  • Screenshot_20210124_134745_com.android.chrome.jpg
    Screenshot_20210124_134745_com.android.chrome.jpg
    322.4 KB · Views: 16
Fitted a tall radiator in our bathroom (not that brand) on our one-pipe system, and it didn't want to heat. Finally I 'throttled' the straight through pipe to divert water into the radiator, and of course it worked fine. Not too much of a problem for us as this 'zone' of our system only feeds one other room.
I would be wary of whether this is going to work For you.
 
Thanks why do the tall ones tend to struggle on a one pipe system? Putting a valve on the straight through pipe many not be great as there will be no access to the pipes underneath the floor afterwards. Laminate going down.
 
Thanks why do the tall ones tend to struggle on a one pipe system? Putting a valve on the straight through pipe many not be great as there will be no access to the pipes underneath the floor afterwards. Laminate going down.
You could use one of the Caleffi one-pipe valves, where you don't have a 'straight-through' pipe (other than what goes on inside the valve), so nothing needed under the floor, not even a pipe! The thermostatic version effectively acts as a diverter. There are other styles, and other brands.

This is the sort of thing I was thinking of:

but not sure how well this might work with a tall rad!
 
You could use one of the Caleffi one-pipe valves, where you don't have a 'straight-through' pipe (other than what goes on inside the valve), so nothing needed under the floor, not even a pipe! The thermostatic version effectively acts as a diverter. There are other styles, and other brands.

This is the sort of thing I was thinking of:

but not sure how well this might work with a tall rad!
Why is it that tall rads. Struggle on a one pipe system? Is it because the water isnt pumped through the rad. It relies on convection?
 
Why is it that tall rads. Struggle on a one pipe system? Is it because the water isnt pumped through the rad. It relies on convection?
It is indeed claimed that circulation is due to convection, but I would have thought if that's the case, a taller radiator might work at least as well as a short one. I don't know enough about fluid dynamics to answer.
 

Similar plumbing topics

  • Question
Thanks for the replies I decided to reroute...
Replies
3
Views
268
  • Question
Who said anything about heating the kitchen ...
Replies
3
Views
591
  • Question
You can buy a replacement bleed screw, but...
Replies
1
Views
471
  • Question
Best you contact Daikin and see what they say...
Replies
4
Views
612
  • Question
Your over thinking this do as I said the...
Replies
9
Views
1K
Back
Top