Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Open vent DHW - calculate recovery time in the Central Heating Forum area at Plumbers Forums

Messages
58
What would be the heating time for this (indirect) vented cylinder? Rated coil = 14kw
Is it 96 litres x 4.2 specific weight x 40 (dT) ? How do I calculate the heating requirement of the boiler to heat this cylinder.
Secondly, they are simpler to install as opposed to unvented type but what are the advantages they have over their unvented cousins?
Thanks in advance for guidance.
 

Attachments

  • vented cylinder.png
    vented cylinder.png
    1 MB · Views: 48
Not sure but my old college books all say allow 3kw for the cylinder

They have no advantages over an unvented. You would only fit a vented one if you didn't have means of getting a relief pipe out, the plumbing in the house is Rubbish or the water pressure and flow are not adequate
 
to heat 96l at dt40 your coil is only 14kw so around the 20-25mins mark
 
eg

20mins x60 second =1200 seconds
4.2 x96x40 / 1200 = 13.4kw at 20 mins
 
Thank you both of you.
The coil rating is possibly based on a 80C boiler temperature and a flowrate of maybe 30LPM which may not be the normal running conditions so maybe average coil rating of 8 to 10kw, still only a problem if you are programming the reheat time, maybe allow say 30/35 minutes in the summer and 40/45 minutes in the winter.
 
The coil rating is possibly based on a 80C boiler temperature and a flowrate of maybe 30LPM which may not be the normal running conditions so maybe average coil rating of 8 to 10kw, still only a problem if you are programming the reheat time, maybe allow say 30/35 minutes in the summer and 40/45 minutes in the winter.
Thank you Sir.
 

Similar plumbing topics

It doesn’t mean you will have lower temps. It...
Replies
4
Views
3K
Is there a standard for the above?, ie...
Replies
0
Views
660
Again, without an idea of system volume we're...
Replies
16
Views
4K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
855
HRP123
H
Back
Top