Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss OV system banging noise at boiler. Happened a few times, likely cause? in the Boilers area at Plumbers Forums

Status
Not open for further replies.

armyash

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
2,650
Hi guys as above really, been to a couple of jobs where there has been a banging noise at the boiler on an OV system. everything is circulating ok and getting hot but occasionally there's a banging noise coming from the boiler.

What can cause this? muck in the system? Struggling pump?

Thanks
 
Without thinking of the obvious it could be no bypass on system so if both 2 ports shut down it can cause a clunking noise or sludged heat exchanger
 
Are they old cast iron heat exchangers? Gravity hot water?

It's mostly sludge on old stuff, can be pumps. If it's running ok then leave well alone you'll create problems.

If it ain't broke don't fix it!
 
Are they old cast iron heat exchangers? Gravity hot water?

It's mostly sludge on old stuff, can be pumps. If it's running ok then leave well alone you'll create problems.

If it ain't broke don't fix it!

The latest was a Worcester RI.

Leave it well alone I did, i advised that as it's currently working and i haven't heard the banging myself it's not worth messing with as i could cause an issue.

Just asking out of interest more than anything as it's annoying going to jobs where it's all working but the customer says there's something wrong. I tell them if it's all working, there is nothing for me to fix and the noise they hear could be a number of things but not worth messing with as could create a bigger problem than just noise.
 
New boilers?

somethings overheating but the cause could be numerous things, faulty stat, poor circulation etc
 
I've seen numerous Worcester Ri with crossed flow and return that do this. Partly because of the stupid arrows they put on the chassis that don't match up if you take the pipes up the back!

boiler seems to work fine but the thermistor is measuring the return temp so can boil if flow temp is excessive.
 
Someone forgot to wire the pump from the boiler to provide overrun had that a few times.

Blocked/restricted h plan

zone valve upside down

zone valve too close to the pump

no system bypass

lack of water in the system
 
cheers for the excellent replies, plenty for me to keep an eye out for.
 
Status
Not open for further replies.

Similar plumbing topics

No problem. Nice to be thanked and appreciated...
Replies
5
Views
1K
Deleted member 120897
D
Np Simon. Hoping to get the boiler engineer...
Replies
4
Views
883
Just for completion, and to have this archived...
Replies
8
Views
2K
Thanks for your reply. The noise is right at...
Replies
2
Views
1K
Whoops, yes, well spotted. Getting my systems...
Replies
6
Views
2K
Back
Top