Partial drain down ch Combi system? | UK Plumbers Forums | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Partial drain down ch Combi system? in the UK Plumbers Forums area at Plumbers Forums

Messages
16
I need to remove a short section of pipe between two rads on the ground floor.
Will this work?
Close off all rads (14) (I have decorator caps), drain down remaining water, carry out repair and refill with internal filling loop.
It's a Worcester Combi boiler about 7 years old, regularly serviced.
Many thanks
 
1. Should be OK provided the valves on all the radiators actually stop all water flow. Presumably you are doing it this way to save adding new inhibitor.
2. If you are going to be doing any soldering, the slightest trace of water in the pipes will stop you. In this case probably better to drain down completely.
 