scoullar

have another problem with a pott performa 24 tap running boiler ignite for about 30 secs and cuts out and ignites again after about 2 mins havnt done any checks yet going tomorrow im thinking diverter or hw sensor or hw plate which is most likely in your experience
 
you need to test all 3 its very common to just be a pinholed diaphragm,if the flow is getting very hot suspect the plate heat or diverter thermister wont be in question the 24kw only has a primary ntc so if heatings working rule that out
 
flame failure lockout was due to pcb that probs solved changed diverter and hot water section water is coming out luke warm intermittently and left hand heating pipe is getting hot could the new diverter be faulty never had new one faulty before
 