Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Performa 28 hw works ch kicks in but does not circulate please advise in the Gaining Plumbing Experience area at Plumbers Forums

Y

yzor

Hello,

I have a Potterton Performa 28.
The hot water works perfectly. The problem I have is with the central heating, it does not circulate the heated water. When I switch the CH on the temp increases to 80 degrees in about 20 seconds and then cuts the boiler out for a couple of mins, it then restarts with the same problem.


The CH flow pipe heats up but it seems the return is not working.

I checked the pump via the vent screw with a screwdriver and stopped the pump without much force. I have replaced the pump with a new one but still have the same problem.

Could it be the PCB?

Can anyone please shed some light.
 
Hello and thanks for your reply.

The pump is installed properly, air has been taken out. Ive checked for blockage hardly any sludge.


"high limit stats,test for restinace"
Please clarify!!
 
i beleive these boilers are supplied with valves that have filters inside them,shut off valves,drain down boiler and clean out filter inside return valve...ive had this problem before and doing this solved the problem.
 
i beleive these boilers are supplied with valves that have filters inside them,shut off valves,drain down boiler and clean out filter inside return valve...ive had this problem before and doing this solved the problem.

spot on moogwai the return filters got crud in it
 

Similar plumbing topics

M
Hello, We’ve recently moved into a fairly old...
Replies
0
Views
589
MartinPod81
M
A
Not sure why you’d replace the pcb without due...
Replies
1
Views
845
Deleted member 120897
D
  • Locked
I would suggest you contact gas safe to report...
Replies
3
Views
545
Back
Top