Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Pipe fall from WC outlet to soil stack in the Boilers area at Plumbers Forums

Status
Not open for further replies.
G

gemwand

I am fitting a new toilet into an existing cast iron stack, but in a new position so the stack has been partially dismantled and I have the luxury of being able to design the falls any way I want.

Can anybody advise on what appropriate falls are? There are lots of recommendations, but not all compatible, and little hard information on why the recommendations are as they are.

The old BS toilet specification had an angle at the WC outlet of 14 degrees, that equates to a fall near the outlet of about 1 in 4.

The standard soil stack branch is at an angle of 92.5 degrees, i.e. a slope in the branch of 2.5 degrees. This seems to be linked to one of the standard rules of thumb, half an inch fall for every foot of pipe (imperial), or 1 in 25 (metric).

Another rule of thumb is a fall of 1 in 40, which derives from Maguire's rule for self-cleansing in drain pipes with intermittent flow (fall = radius in mm/2.5).

The new BS 5503 has horizontal WC outlets. The part H building regulations give a fall of between 18mm and 90mm per metre for branch discharge pipes.

I believe that the old standard installations were designed to have a relatively rapid fall (1 in 4) from the WC outlet into to the soil branch, followed by a bend and then a shallower 1 in 24 fall to the main stack.

Can anyone say what (if anything) was wrong with that? Why do people now appear to recommend much shallower falls, particularly from the WC outlet?
 
Larger diameter pipes. Old cast often had only a 3" branch.

92.5 degrees is fine in 110mm plastic from the wc to through the wall, massive fall not required here as flush impetus is still strong. An appropriate fall Will then need to be obtained from that point depending on the stack position
 
Status
Not open for further replies.

Similar plumbing topics

Should have added in, naturally there will be...
Replies
3
Views
1K
10 o’clock / 45 degrees would be better than...
Replies
3
Views
577
You can actually get 90 degree bends too...
Replies
5
Views
1K
Deleted member 120897
D
Yes or as your first drawing but with an...
Replies
6
Views
2K
Back
Top