Hello fella's, was wondering if anyone might take the time to confirm / refute the following....
The engineer that I am working with and I are starting a job on Monday, old three story building being converted into 4 flats, all old pipework etc being ripped out and everything going in new. The buiding has a cupboard outside the front door containing 4 new gas meters. I'm working out gas pipe runs and sizing for the installation and the first floor flat is an issue....
The only gas appliances going in each flat are Worcester Bosch 24i Greenstar combi's, all other appliances are electric. On that basis, I'm working out that I need a flow rate of 2.87m3/hour minimum, (I've not factored in any extra for possible future requirements) There is a total of 6mtr of 35mm pipe from the meter to run outside the building (inc fittings allowance) before it taps into the wall into the bedroom of the flat. From inside the bedroom, it will reduce down to 28mm and have an AECV and test point (another question there later) and it then has to run a total of 26.5mtr through the flat to the kitchen at the back. Then there is a final 2mtr run of 22mm up the wall into boiler
Using the flow rate tables, I'm calculating a drop in mbar of 0.20 for the 35mm run, 0.88 for the 28mm run & 0.1 for the 22mm......which is a total pressure drop of 1.18mbar....
However, firstly, am I right in assuming that the pressure drops are only applicable to horizontal pipe runs, in which case I can take out of the calculation 4.5mtr of the 35mm which, (without boring you with all the calculations) will give a revised total pressure drop of 1.03mbar.......
Either way, I'd be much happier if my total pressure drop was around 0.8mbar, as it is for all the other flats......so what I'm asking fella's, is in the 'real world', will this calculation prove to be precise in its figures and I have to extend the 35mm run for longer, or is it likely that the maths err on the side of caution and a calculated 1.08mbar drop is worth gambling on ?
Finally, I've got to put a test point downstream and adjacent to the AECV, anyone know if/where you can get a 28mm test point coupling ? I can get them in 15 & 22mm, but not bigger ? Its either that or a 26mtr length of neoprene hose for the AECV let by test...............
Would appreciate any comments, thanks fella's..
The engineer that I am working with and I are starting a job on Monday, old three story building being converted into 4 flats, all old pipework etc being ripped out and everything going in new. The buiding has a cupboard outside the front door containing 4 new gas meters. I'm working out gas pipe runs and sizing for the installation and the first floor flat is an issue....
The only gas appliances going in each flat are Worcester Bosch 24i Greenstar combi's, all other appliances are electric. On that basis, I'm working out that I need a flow rate of 2.87m3/hour minimum, (I've not factored in any extra for possible future requirements) There is a total of 6mtr of 35mm pipe from the meter to run outside the building (inc fittings allowance) before it taps into the wall into the bedroom of the flat. From inside the bedroom, it will reduce down to 28mm and have an AECV and test point (another question there later) and it then has to run a total of 26.5mtr through the flat to the kitchen at the back. Then there is a final 2mtr run of 22mm up the wall into boiler
Using the flow rate tables, I'm calculating a drop in mbar of 0.20 for the 35mm run, 0.88 for the 28mm run & 0.1 for the 22mm......which is a total pressure drop of 1.18mbar....
However, firstly, am I right in assuming that the pressure drops are only applicable to horizontal pipe runs, in which case I can take out of the calculation 4.5mtr of the 35mm which, (without boring you with all the calculations) will give a revised total pressure drop of 1.03mbar.......
Either way, I'd be much happier if my total pressure drop was around 0.8mbar, as it is for all the other flats......so what I'm asking fella's, is in the 'real world', will this calculation prove to be precise in its figures and I have to extend the 35mm run for longer, or is it likely that the maths err on the side of caution and a calculated 1.08mbar drop is worth gambling on ?
Finally, I've got to put a test point downstream and adjacent to the AECV, anyone know if/where you can get a 28mm test point coupling ? I can get them in 15 & 22mm, but not bigger ? Its either that or a 26mtr length of neoprene hose for the AECV let by test...............
Would appreciate any comments, thanks fella's..