- Messages
- 55
Hi all, still working on my portfolio but having a bit of confusion regarding allowances for fittings when working out pipe size requirements as I'm reading conflicting information. In college we were told to allow 0.5m for Tees and elbows and 0.3m for bends. My Viper gas handbook says the same but only up to 28mm but doesn't say anything about 35mm, whereas my BPEC book gives completely different values going as high as 3m for a 35mm Tee with the flow exiting into the branch. I appreciate that it's the end result that is important and so long as there is less than 1mb drop at the appliance it will be fine but I'd like to be able to be sure the installation designed is going to work before I put it in.
The specific case I'm looking at is proving quite tricky to me as its an extended bungalow with two boilers, one at one end, the other in the middle, a cooker in the middle but on the opposite side and the meter at the other end so the runs are rather long.
The specific case I'm looking at is proving quite tricky to me as its an extended bungalow with two boilers, one at one end, the other in the middle, a cooker in the middle but on the opposite side and the meter at the other end so the runs are rather long.