plumbbobshan
Gas Engineer
- Messages
- 77
Evening lads and lasses ,
My mate has a Potterton Apollo ,with the following symptom :-
Run hot water all day long, put the heating on and it blows off at 2.8 bar .
When its cold the pressure sits at 1.2bar .
Have replaced the expansion vessel as it was found to be bust.
Replaced the PRV as it was passing .
Checked the pressure in the new expansion vessel and set it to 1bar as the label states . Put the heating on and it blows off .
Installed in a small bungalow with 5 rads .
any ideas ????
thanks in anticipation.