B

boilkermansab

Recently having problems with my envoy, the condensate was backing up and fllooding the boiler, so i tried cleaning the syphon but it was still the same.
Ended up buying a new one, however it seems to be doing the same and not letting the condense run away. But if i go to undo the drain pipe where it connects to the syphon it begins to run away. Seems as if it causes some sort of air lock??
Anyone else encounted this??
I know this boilers are not the best but we have had it 10 years and its only the 2nd time its let us down
 
make sure you havnt created a double syphon, if you have, it wont drain the 1st siphon until the height of water in trap 1 - equals the height of the trap depth in siphon 1 plus trap depth in siphon 2
 
I can see what your getting at but how have i created a double syphon??


I deal with industrial boilers, so househould is not my forte!
 
Last edited by a moderator:
The little black ribbed rubber connection is blocked (sounds like something for the weekend!!). There is more to check internally but seals MUST be replaced.
 
Status
Not open for further replies.

Similar plumbing topics

Hi I have been ringing round trying to have...
Replies
0
Views
609
This response doesn't make any sense, as the...
Replies
23
Views
2K
Thank you for the detailed and considered...
Replies
14
Views
2K
Just to round this off with what I found here...
Replies
5
Views
781
R
Hi, thanks for your answer. It does not have...
Replies
2
Views
2K
Renato
R
Back
Top