Potterton Gold heat only, I went there last week no heating, 2 jammed trv's and air in the system. I was up against it, it was late and I had 3 jobs ahead of me. Boiler fired up rads got hot, hung around 10 minutes, all good. Tenant reported magnetic filter leaking, put in quote to replace. Got sent back today to do but was told heating issue again can I sort while i'm there??.
So I found out a Honeywell thermostat was fitted before I went last week as the old one was making a funny noise apparently then the heating issues started a day or 2 after. The tenant said the guy who changed had a hard time of it getting the heating working. Seems a bit strange.
First off. all off at mains, switch on, ch and hw both switched off at the programmer and the boiler fires up and goes round hot water. 3 port by the way.
If I push the lever over on 3 port, it will circulate round the heating system. Sometimes it will stay on for a while, other times goes off after a minute.
Phoned technical who said check the 4 way junction box inside case. In the S/L terminal there was a permanent live so he said take that out and see what happens.
Ok no permanent live with switch live now. HW will now switch on at programmer.
No change for ch, turn ch on at programmer I dont get 240 on orange. I tried a new actuator and no different.
Person who changed room stat didnt do anything at wiring center or boiler. allegedly.
Is this pointing to programmer or something else?
Thanks.
So I found out a Honeywell thermostat was fitted before I went last week as the old one was making a funny noise apparently then the heating issues started a day or 2 after. The tenant said the guy who changed had a hard time of it getting the heating working. Seems a bit strange.
First off. all off at mains, switch on, ch and hw both switched off at the programmer and the boiler fires up and goes round hot water. 3 port by the way.
If I push the lever over on 3 port, it will circulate round the heating system. Sometimes it will stay on for a while, other times goes off after a minute.
Phoned technical who said check the 4 way junction box inside case. In the S/L terminal there was a permanent live so he said take that out and see what happens.
Ok no permanent live with switch live now. HW will now switch on at programmer.
No change for ch, turn ch on at programmer I dont get 240 on orange. I tried a new actuator and no different.
Person who changed room stat didnt do anything at wiring center or boiler. allegedly.
Is this pointing to programmer or something else?
Thanks.