I have got an ongoing issue with a prima 60F. Before I looked at it, someone had replaced the boiler stat and the overheat stat and the system had been cleaned. The problem is it keeps tripping the overheat stat, but not all the time, maybe once every 2-3 days.
I found the inner flue was corroded through, so that got sorted and burner pressure and gas rate checked, all ok. Heat exchanger and burner cleaned. This seemed to solve the problem for about 6 months, then I got a call to say it was playing up again. I found the pump to be noisy so that was replaced and is now working fine. Again the boiler was ok for about 4-6 months.
It is now overheating again. The fan is a little noisy, but could the fan running a bit slow cause an over heat fault on these? All settings are ok, good circulation etc. I have never actually seen it overheat and trip the stat, but its normally right at the end of the night when its been running for a while as they say they don't notice the boiler go off and just notice that is doesn't fire in the morning and the overheat needs to be reset for it to fire.
Any suggestions on what to test or check next?
I found the inner flue was corroded through, so that got sorted and burner pressure and gas rate checked, all ok. Heat exchanger and burner cleaned. This seemed to solve the problem for about 6 months, then I got a call to say it was playing up again. I found the pump to be noisy so that was replaced and is now working fine. Again the boiler was ok for about 4-6 months.
It is now overheating again. The fan is a little noisy, but could the fan running a bit slow cause an over heat fault on these? All settings are ok, good circulation etc. I have never actually seen it overheat and trip the stat, but its normally right at the end of the night when its been running for a while as they say they don't notice the boiler go off and just notice that is doesn't fire in the morning and the overheat needs to be reset for it to fire.
Any suggestions on what to test or check next?