I have seen a few threads regarding these boilers but none seem to quite match my sympton.
Normally when the room stat or cylinder call for heat I see/hear the fan start, the pilot lights and then the main burner. Which I guess is normal operation.
But sometimes the main burner only stays lit for maybe a minute and goes out leaving the pilot lit?
I checked the solenoid coil volts and I have 230 on the blue common to both coils and 3 to 5 volts on the pilot (black wire) and main valve (white wire) other connection when the flames are lit. I guess this means they are switched on the neutral side of the coil?
Either way as the main burner goes out (leaving the pilot lit) the voltage on the white terminal rises to 230. I take this to mean that the pcb has decided to turn off the main burner?
I thought last week I had a pump problem or restiriction so replaced the pump and added a litre of X400 today but the problem is so far unchanged. Both up & down rad returns warm up reasonably quickly and the DWH return even quicker.
System is vented, 3 port valve with indirect HW cylinder. All seems to function properly when the boiler lights.
If anyone has any thoughts on what I could do next I'd appreciate hearing.
Thanks,
Steve.
Normally when the room stat or cylinder call for heat I see/hear the fan start, the pilot lights and then the main burner. Which I guess is normal operation.
But sometimes the main burner only stays lit for maybe a minute and goes out leaving the pilot lit?
I checked the solenoid coil volts and I have 230 on the blue common to both coils and 3 to 5 volts on the pilot (black wire) and main valve (white wire) other connection when the flames are lit. I guess this means they are switched on the neutral side of the coil?
Either way as the main burner goes out (leaving the pilot lit) the voltage on the white terminal rises to 230. I take this to mean that the pcb has decided to turn off the main burner?
I thought last week I had a pump problem or restiriction so replaced the pump and added a litre of X400 today but the problem is so far unchanged. Both up & down rad returns warm up reasonably quickly and the DWH return even quicker.
System is vented, 3 port valve with indirect HW cylinder. All seems to function properly when the boiler lights.
If anyone has any thoughts on what I could do next I'd appreciate hearing.
Thanks,
Steve.