Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Potterton promax in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

hammers4spanner

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
7,703
Had a call to one of these earlier 6 years old intermittent e133 fault (interrupted gas supply) from fault code.

Boiler goes through sequence everything calling , pump spins ,fan spins but can't here it sparking , pulled out probes didn't look like anything was wrong gap looked ok not overly dirty.

Checked the terminals off the board think 1/5 and had little DC current was initially thinking gas valve but now thinking board .

Any you agree?
 
100% sure about electrodes? Can fit a pound coin in gap? Continuity ok?
High and low CO set up perfectly?
Condensate pipework clear?
 
Im not 100% sure thats why asked on here , was a gap between electrodes but would say not big enough to pop pound coin through.
Wouldn't even flash flash up to check CO and condensate clear .
 
You know what never even thought about that , got a bit tunnel vision on the pcb
 
If a pound coin dose not fit tight in electrode gap they may be knackered.
You check for continuity through the electrode?

100vdc across X2 connector terminals 2 & 5 or the board may be gone.
 
Only got 15 dc over the terminals which made me think the board may have an issue from then got a bit tunnel vision ,

One of those turned up to do a service 'oh hello your boiler don't work'
 
Status
Not open for further replies.

Similar plumbing topics

J
According to the manual it’s 5 & 6 for CH...
Replies
1
Views
572
Deleted member 120897
D
Thanks some good ideas. Just as an aside if we...
Replies
10
Views
2K
I don’t think there are any other checks on...
Replies
7
Views
158
Burger
B
Your gas rate is your big one to check. Well...
Replies
9
Views
163
Keep a diary recording the dates/times of when...
Replies
5
Views
3K
Back
Top