Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Pressure Dropping on Combi boiler circuit in the Boilers area at Plumbers Forums

Status
Not open for further replies.
P

peterx666

Have a Halstead Ace High boiler and enclosed combi circuit problem

I I up the pressure to 1 bar and leave boiler shut off overnight it is still 1 bar in the morning

When the boiler runs the pressure goes up to 2 bar or over After the thing has run a while and it shuts off on the timer the pressure drops to around 1/2 bar

My question before I start ripping up floor boards - is it always a leak in the pipework?

Any comment or advice appreciated

pete
 
Hi pete ... floorboards are your last resort IMO :)

Are you gas safe registered? Compitent? know a bit here and there ... lol?
 
Definitely no water coming from PRV pipe outside? Would get boiler checked out first.

If all ok then must be a system leak and may have to start lifting those boards.
 
Sounds like a boiler fault not pipes, if only when it's running expansion vessel is favourite for causing that what you,v described. Get a GSE mate.. Leave ya boards for now. (Gas safe Engineer).
 
Yes noticed the pipe was dripping but not seen a lot coming from it?
 
it doesnt need a lot to drop the preasure you need a new prv and getr the pv checked at the same time
 
It dose sound like your expansion vessel,s gone and releasing through the Prv,,
like Steve said, new Prv and check/recharge expansion vessel.
 
Status
Not open for further replies.

Similar plumbing topics

the pressure of my boiler looks unstable...
Replies
0
Views
665
That means you have a leak as the system...
Replies
9
Views
829
J
Thanks! much appreciated :)
Replies
2
Views
741
Joey T
J
Fits back on flue on top of boiler
Replies
3
Views
625
You need a new service engineer not a new...
Replies
3
Views
938
Back
Top