Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Pressure release valve on converted vented system in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
45
Folks

A customer pointed out a small drip from an overflow pipe coming from a pressure release valve of a heating system they have had converted from being a vented system. The issue would seem to be that the pressure release valve (3 bar is letting by).

My intention was simply to go in and replace their PRV. However it occurs to me that 3 bar seems a little low and is quite likely to blow with the least variation in the water pressure* and hence subsequently let by. Should I maybe install a slightly higher pressure PRV this time or perhaps you might have some other suggestion?

Many thanks

Michael

*They are mind you, 2/3 the way up on a hill which probably means that pressure is generally a little on the low side.
 
:iagree: your post shows up a great lack of knowledge michcosg. I'd advise that you go no further, explain to your customer that your knowledge is limited and would advise that they get someone else to look at the problem!!
 
michcosg, just wondering if you could tell us why the pressure 'relief' valve is 3 bar :)
 
Hi MIchel ,

I know Michel we worked together on a site about three weeks ago . Michel does not have a much experience but is a good person .
Michel as above , it will be better if a heating engineer have a look .

Stan
 
Last edited:
Hi MIchel ,

I know Michel we worked together on a site about three weeks ago . Michel does not have a much experience but is a good person .
Michel as above , it will be better if a heating engineer have a look .

Stan




Must still be lots of work going on down there if ''Michel'' is still in work
 
Hi MIchel ,

I know Michel we worked together on a site about three weeks ago . Michel does not have a much experience but is a good person .
Michel as above , it will be better if a heating engineer have a look .

Stan

I think Michel got the message Stan? Hopefully we haven't put him off coming back :) We've all got to learn somehow and this place offers the avenue to learn if you can take the flack now and again :)
 
I spoke to Michel and invited him here to be regular as he will have ability to learn the theory hear , practice as I advised him I will take him on when I get some business going as I have finished the 8 houses and the builder is not doing any more
 
It all comes with experience i hope he gets the chance to achieve his goals in these tight times
 
Yes OK its been about a month since I looked at this side issue whilst looking at a few other problems with their taps etc. And yes I accept I am not Gas Safe and have limited exposure to diagnosing a fault with a converted system such as this.

It would seem on reflection that I have confused the pressure release valve on a mains supply into an unvented cylinder with the pressure release valve on a now closed heating circuit.

To answer Bob the plumbers question: why do I think the pressure 'relief' valve is set to 3 bar - I would have said that is to protect the conventional copper cyclinder. Still seems a bit low to me but notice that the PRV on my combi is also 3 bar so I guess its about right!

However I would ask the question, is really necessary to have someone of considerably more experience in this area to swap out a faulty part? Non Gas Safe plumbers engage with heating systems in many ways I am sure. Have you always known so much about something you have explored? I accept I could do with some guidance. However are people suggesting, that given what I have now stated here, still betrays an unacceptable level of understanding?

That said I do appreciate the feedback and will consider passing this job to Gas Safe colleague if that seems to be the consensus.

Many thanks
 
michcosg, i dont think theres anything wrong with changing a part. But i believe you need to know why it needs changing and what the implications are if you change it for something that is or isnt correct, thats where the training comes in. In this instance you looked at a converted open vented system, so prv is external to regular /standard boiler generally. It could have an expansion problem which has caused it to drip/pass albeit just a knackered prv?? in changing the prv to a higher limited prv say 6 bar or more it would be the entire system that has to contain that excess pressure thus putting massive strain on pipe work and the integrity of the boiler and parts. next thing you know prv has not blown off ...but part of the pipe work or boiler in the house causing a terrible mess at the least, and if its overheating its extremely dangerous!. know you limits, there is stuff out there that even myself as a qualified engineer would walk away from maybe because im not 100% sure and wouldnt take the risk, but im in a better postition to ask with my current experience and qualifications, its knowing your limits like i said...stick to what you know. safegas says your a good lad, so i know you will not mess around with it because you know know the risks enough to decided against it :)
 
Thanks Bob

Yes that is a fair point, that there could be a problem with the expansion vessel and indeed so too are your concerns about installing a PRV with a higher pressure threshold. However withstanding my initial mis-description of the issue, part of the reason I think I checked before increasing the size of the valve, was because I realised this was a 'significant change' to the system and therefore needed checking. Changing a PRV (like for like) and indeed checking a pressure vessel are not in my view, significant changes.

I accept though this is new ground for me. I do have some training however - unvented and solar tickets but admit have only applied them to a limited extent. Still maybe I should get a more experienced colleague to at least check my intentions on this occassion.

Thanks again for you input.

M.
 
Yes OK its been about a month since I looked at this side issue whilst looking at a few other problems with their taps etc. And yes I accept I am not Gas Safe and have limited exposure to diagnosing a fault with a converted system such as this.

It would seem on reflection that I have confused the pressure release valve on a mains supply into an unvented cylinder with the pressure release valve on a now closed heating circuit.

To answer Bob the plumbers question: why do I think the pressure 'relief' valve is set to 3 bar - I would have said that is to protect the conventional copper cyclinder. Still seems a bit low to me but notice that the PRV on my combi is also 3 bar so I guess its about right!

However I would ask the question, is really necessary to have someone of considerably more experience in this area to swap out a faulty part? Non Gas Safe plumbers engage with heating systems in many ways I am sure. Have you always known so much about something you have explored? I accept I could do with some guidance. However are people suggesting, that given what I have now stated here, still betrays an unacceptable level of understanding?

That said I do appreciate the feedback and will consider passing this job to Gas Safe colleague if that seems to be the consensus.

Many thanks

Michcosg,

I appreciate you have an unvented ticket but if you don't know what the root causes of a T/PRV leak can be, I would get someone in. There are 6 things that would cause the pressure relief valve to leak: -

1.) Pressure reducing valve on inlet control group has failed.
2.) Expansion valve has scaled up, stopping the seal from seating.
3.) Expansion vessel has lost it's charge (maybe air has not been topped up or air/water seal has ruptured).
4.) Cylinder is being back-pressured by mixer taps/showers that don't have a balanced feed.
5.) Expansion vessel installed upstream of the check valve on the inlet control group (I have seen this before).
6.) Cylinder high temperature. This will cause an increase in pressure that will activate the pressure relief valve (it opens at a lower pressure than the TRV).

As you can see there is a lot to investigate. If you are at all in doubt get someone in to help with more experience. Your idea of replacing the EV with one rated for a higher pressure is extremely dangerous. The fact you would even consider it says that (I'm sure with the best intentions) you should not be working on this yourself.

You don't need a gas safe registered engineer for this as the problem is nothing to do with any gas appliance. You just need a competent plumber with an unvented ticket to help you out. Get them in and learn from them. As you are new it may be handy to have a more experienced plumber in your area that you can pass jobs too when you are out of your depth, on the understanding that you can learn from them (i.e. watch and ask questions).

Please get someone else in and learn from them on this one!
 
Last edited:
Michcosg,

I appreciate you have an unvented ticket but if you don't know what the root causes of a T/PRV leak can be, I would get someone in. There are 6 things that would cause the pressure relief valve to leak: -

1.) Pressure reducing valve on inlet control group has failed.
2.) Expansion valve has scaled up, stopping the seal from seating.
3.) Expansion vessel has lost it's charge (maybe air has not been topped up or air/water seal has ruptured).
4.) Cylinder is being back-pressured by mixer taps/showers that don't have a balanced feed.
5.) Expansion vessel installed upstream of the check valve on the inlet control group (I have seen this before).
6.) Cylinder high temperature. This will cause an increase in pressure that will activate the pressure relief valve (it opens at a lower pressure than the TRV).

As you can see there is a lot to investigate. If you are at all in doubt get someone in to help with more experience. Your idea of replacing the EV with one rated for a higher pressure is extremely dangerous. The fact you would even consider it says that (I'm sure with the best intentions) you should not be working on this yourself.

You don't need a gas safe registered engineer for this as the problem is nothing to do with any gas appliance. You just need a competent plumber with an unvented ticket to help you out. Get them in and learn from them. As you are new it may be handy to have a more experienced plumber in your area that you can pass jobs too when you are out of your depth, on the understanding that you can learn from them (i.e. watch and ask questions).

Please get someone else in and learn from them on this one!

Excellent post, saved me getting on my soap box, people having a go at the op, must be gas safe etc.

I'm glad I continued to read the answers people had posted.
 
Michcosg,

I appreciate you have an unvented ticket but if you don't know what the root causes of a T/PRV leak can be, I would get someone in. There are 6 things that would cause the pressure relief valve to leak: -

1.) Pressure reducing valve on inlet control group has failed.
2.) Expansion valve has scaled up, stopping the seal from seating.
3.) Expansion vessel has lost it's charge (maybe air has not been topped up or air/water seal has ruptured).
4.) Cylinder is being back-pressured by mixer taps/showers that don't have a balanced feed.
5.) Expansion vessel installed upstream of the check valve on the inlet control group (I have seen this before).
6.) Cylinder high temperature. This will cause an increase in pressure that will activate the pressure relief valve (it opens at a lower pressure than the TRV).

As you can see there is a lot to investigate. If you are at all in doubt get someone in to help with more experience. Your idea of replacing the EV with one rated for a higher pressure is extremely dangerous. The fact you would even consider it says that (I'm sure with the best intentions) you should not be working on this yourself.

You don't need a gas safe registered engineer for this as the problem is nothing to do with any gas appliance. You just need a competent plumber with an unvented ticket to help you out. Get them in and learn from them. As you are new it may be handy to have a more experienced plumber in your area that you can pass jobs too when you are out of your depth, on the understanding that you can learn from them (i.e. watch and ask questions).

Please get someone else in and learn from them on this one!

All very informative but not actually pertinent in this case as the leak is from a PRV on a sealed heating system.
 
My understanding is he thought it was then realised it was coming from an unvented cylinder setup. If I'm wrong then my post is indeed fairly useless!
 
Yes OK its been about a month since I looked at this side issue whilst looking at a few other problems with their taps etc. And yes I accept I am not Gas Safe and have limited exposure to diagnosing a fault with a converted system such as this.

It would seem on reflection that I have confused the pressure release valve on a mains supply into an unvented cylinder with the pressure release valve on a now closed heating circuit.

To answer Bob the plumbers question: why do I think the pressure 'relief' valve is set to 3 bar - I would have said that is to protect the conventional copper cyclinder. Still seems a bit low to me but notice that the PRV on my combi is also 3 bar so I guess its about right!

However I would ask the question, is really necessary to have someone of considerably more experience in this area to swap out a faulty part? Non Gas Safe plumbers engage with heating systems in many ways I am sure. Have you always known so much about something you have explored? I accept I could do with some guidance. However are people suggesting, that given what I have now stated here, still betrays an unacceptable level of understanding?

That said I do appreciate the feedback and will consider passing this job to Gas Safe colleague if that seems to be the consensus.

Many thanks

As he stated in his post above, he initially thought it was as Mike Jackson suggested but his later post indicates that it's the pressure relief valve on an unvented cylinder...
 
You have to ask yourself what has caused it to leak? Has the boiler/system overheated? What has caused it to over heat? Is the expansion vessel correctly sized? But usually when changing prv's on domestic systems, especially when converted they are specified at 3bar. I would not advise fitting a higher bar eg. 5 bar prv. Higher bar prv's are usually fitted on unvented systems.
 
Status
Not open for further replies.

Similar plumbing topics

That means you have a leak as the system...
Replies
9
Views
812
Can central heating / gas engineer expert help...
Replies
0
Views
823
    • Funny
  • Question
It’s cheaper to buy an unvented cylinder (8...
Replies
13
Views
2K
  • Question
Yes as they don’t seal after they’ve chucked...
2 3
Replies
54
Views
4K
Replies
4
Views
597
Back
Top