Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Pressure relief valve install in the Plumbing Jobs | The Job-board area at Plumbers Forums

Messages
18
Hi

I will be soon be removing f and e tank and going to mains, i will be installing expansion kit in the cylinder cupboard, my only issue is i have no where to discharge my safety relief,
My question is can anyone see a problem with cutting in prv by the boiler as this would be a better discharge point as right by external wall.

Thanks
 
By law, this work needs to be done by a plumber who is qualified to work on unvented hot water systems (sometimes referred to as having a G3 ticket). They should also be a member of a competent persons' scheme and should be able to advise you on all aspects of the install.
 
By law, this work needs to be done by a plumber who is qualified to work on unvented hot water systems (sometimes referred to as having a G3 ticket). They should also be a member of a competent persons' scheme and should be able to advise you on all aspects of the install.

I’m guessing he means a heating system kit and not an unvented cylinder
 
I am g3 qualified and thats to do with unvented cylinders,sorry i think i posted to wrong forum, this would be a question for a expierence install heating engineer

Thanks anyway

You should know the answer but that’s a no you can’t move the prv away from the unvented cylinder
 
If you're G3 then you should have no problem deciding a suitable location for a PRV, whatever system it's fitted to.

Is the boiler suitable for use in a sealed system?

You may have confused people by saying "f and e tank and going to mains" instead of saying going to a sealed system
 
G3 has nothing to do with my question, yes boiler is suitable but thats not what i was asking, my copper cylinder is compatible as well if u like but thats not what im asking. as i said i posted to wrong group, people dont have the answer on this thread thats why they are going off the point, its fine i know its not a straight forward question,

Ok yes from gravity to sealed if thats where we are going!

Thanks
 
G3 has nothing to do with my question, yes boiler is suitable but thats not what i was asking, my copper cylinder is compatible as well if u like but thats not what im asking. as i said i posted to wrong group, people dont have the answer on this thread thats why they are going off the point, its fine i know its not a straight forward question,

Ok yes from gravity to sealed if thats where we are going!

Thanks

Then yes you can put the prv by the boiler
 
Hi

I will be soon be removing f and e tank and going to mains, i will be installing expansion kit in the cylinder cupboard, my only issue is i have no where to discharge my safety relief,
My question is can anyone see a problem with cutting in prv by the boiler as this would be a better discharge point as right by external wall.

Thanks
To be honest the way you put up the op wrong footed me, I also was confused about your conversion plans. you came to the correct forum be in no doubt of our competance
and now we can see your plans then you will get suitable advice . I would always site the
pressure relief as close to the pressure vessel as possible and with a direct and short path
to the outside...it really is a safety issue which superseeds cosmetics in my opinion
centralheatking
 
Thanks for the reply,

I understand what your saying ,but in theory if i cut in relief valve into return by boiler this in principle is still protecting system at 3 bar no matter where it has been installed on the circuit, my problem is ive never seen it done this way. Only ever seen with ch system kit,eg ex vessel/gauge/ press relief combo. It Would give me peace of mind that someone has done this before.

As i said in previous thread i have no where to discharge safety valve in cylinder cupboard without ripping up carpet etc

Any points anyone has why i cant do this please let me know,

Thanks
 
Thanks for the reply,

I understand what your saying ,but in theory if i cut in relief valve into return by boiler this in principle is still protecting system at 3 bar no matter where it has been installed on the circuit, my problem is ive never seen it done this way. Only ever seen with ch system kit,eg ex vessel/gauge/ press relief combo. It Would give me peace of mind that someone has done this before.

As i said in previous thread i have no where to discharge safety valve in cylinder cupboard without ripping up carpet etc

Any points anyone has why i cant do this please let me know,

Thanks
I am an expert in Pressurised Domestic Heating Systems for various reasons. I think it is dangerous to fit extended remote pressure vent terminals, they ought to go straight out without
any possibility of damage or restriction. I have never seen such an idea but that is not to state you cannot do it ....I would advise NO. centralheatking
 
Hows the house piped up ive seen over flows from f + e tanks and supply drop down from the loft into the a/c.
Under floorboards and outside.
Which you could then pick up and take to drain.
 
Ok thanks for advice

Just so you know, if i install press relief by boiler i will still be discharging to outside.

Also i will be fitting ch system kit upstsirs, filling loop, vessel etc, i will just plug off port for press relief and install by boiler instead

Hope thats more clearer

Also have u got a reason why you believe its unsafe?

Thanks again for advice.

Really appreciate it
[automerge]1572363274[/automerge]
Hows the house piped up ive seen over flows from f + e tanks and supply drop down from the loft into the a/c.
Under floorboards and outside.
Which you could then pick up and take to drain.

Yes mate seen this b4 too but trying to stay away from this idea

Thanks though mate
 
with out knowing your boiler they usually have prv built internally.
Never plug of a prv on your cylinder ticking time bomb if theres a system failure.
Check the mi's of what youre planning on buying.
Far as im concerned all appliances which generate heat or pressure should have a prv fitted to it. Prvs should be fitted where the heat is generated ( appliances)
 
with out knowing your boiler they usually have prv built internally.
Never plug of a prv on your cylinder ticking time bomb if theres a system failure.
Check the mi's of what youre planning on buying.
Far as im concerned all appliances which generate heat or pressure should have a prv fitted to it. Prvs should be fitted where the heat is generated ( appliances)
Sorry mate appreciate help but have u read thread, dident say anything about plugging prv on cylinder, boilers conventional
 
My mistake on that opening line I did see you mentioned it.
Post 19 mate you said you'll just plug off prv and move it next to the boiler.
 
It should be same pressure, what makes you think it will be different?

Thanks
It's all the same pressure Lee just make sure you have no valves or controls on the return back to the boiler you need a open circuit the expansion vessel , pressure gauge , and filling loop will all tee in the return maybe in the airing cupboard . Cheers kop
 

Attachments

  • Screenshot_20191029-180138.png
    Screenshot_20191029-180138.png
    104.4 KB · Views: 20
It's all the same pressure Lee just make sure you have no valves or controls on the return back to the boiler you need a open circuit the expansion vessel , pressure gauge , and filling loop will all tee in the return maybe in the airing cupboard . Cheers kop
Perfect, yes ive checked all that,

Thanks
[automerge]1572373212[/automerge]
Perfect, yes ive checked all that,

Thanks

Just wanted to see if anyone had a legitimate reason not to do this as ive personally never done it

Thanks again
 

Similar plumbing topics

  • Question
If the 'TPR' valve you usually turn to...
Replies
1
Views
639
  • Question
Yes, I have this as well. I called a plumber...
Replies
6
Views
876
Pritesh Patel
P
  • Question
Bottom right is the pump with an auto air vent...
Replies
16
Views
1K
To fully recharge, the lowest hot tap should...
Replies
6
Views
2K
That means you have a leak as the system...
Replies
9
Views
812
Back
Top