Hi all.
Ok. In December I converted an open-vented system into a sealed combi-boiler heating system for a customer. I contracted a GSR engineer to do the boiler installation whilst I modified the pipework on the CH side of things.
The existing pipework was pressure tested to 5 bars for 30 minutes prior to connecting the boiler and there was no pressure drop. This was done with cold water obviously as the boiler wasn't connected (for obvious reason) at the time.
Since installation, the customer is now having to top the pressure up a couple of times a week. I have checked all visible pipework and radiator tails, there are no signs of leakage at all. PRV is not leaking. All the CH pipework runs above ground floor level through the usual arrangement of stud walls, solid walls and floor/ceiling voids. There are no signs of any leakage coming through walls and ceilings.
Given that the pressure is dropping from 1.5 bars to 1 bar every few days I would expect this to be a fairly big leak (if indeed water is leaking) and for it to be very noticeable by now in some way.
I've added 2 cans of Fernox F4 Leak Sealer via the filling loop today and will see what happens over the next couple of weeks.
I checked the radiators today and there are no signs of air in them. I also placed 2x AAR valves at the top of the system where the old open vent and overflow pipes were in the loft space. Due to the existing layout of the current heating system it was not possible to get easy access to the main flow/return pipework these teed off and cut them back there so this was the route I chose.
Does anyone have any other ideas if the leak sealer doesn't sort it out? Could the problem be the expansion vessel?
Ok. In December I converted an open-vented system into a sealed combi-boiler heating system for a customer. I contracted a GSR engineer to do the boiler installation whilst I modified the pipework on the CH side of things.
The existing pipework was pressure tested to 5 bars for 30 minutes prior to connecting the boiler and there was no pressure drop. This was done with cold water obviously as the boiler wasn't connected (for obvious reason) at the time.
Since installation, the customer is now having to top the pressure up a couple of times a week. I have checked all visible pipework and radiator tails, there are no signs of leakage at all. PRV is not leaking. All the CH pipework runs above ground floor level through the usual arrangement of stud walls, solid walls and floor/ceiling voids. There are no signs of any leakage coming through walls and ceilings.
Given that the pressure is dropping from 1.5 bars to 1 bar every few days I would expect this to be a fairly big leak (if indeed water is leaking) and for it to be very noticeable by now in some way.
I've added 2 cans of Fernox F4 Leak Sealer via the filling loop today and will see what happens over the next couple of weeks.
I checked the radiators today and there are no signs of air in them. I also placed 2x AAR valves at the top of the system where the old open vent and overflow pipes were in the loft space. Due to the existing layout of the current heating system it was not possible to get easy access to the main flow/return pipework these teed off and cut them back there so this was the route I chose.
Does anyone have any other ideas if the leak sealer doesn't sort it out? Could the problem be the expansion vessel?