Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Problem with system: boiler only fires up in hw mode in the Boilers area at Plumbers Forums

Status
Not open for further replies.
G

gasfun

Hi,
Went to a customer today. System with heat only boiler. the boiler fires up in hot water demand , but not in ch mode.if hot water and central heating are called for everything works fine. My thoughts are diverter valve. But then boiler would fire up when ch is called for?
 
So has a 3 port valve?
 
Because it saves time in the long run.......

Probably the synchron motor in the 3 port valve has failed. When you select hot water, the boiler will fire without any input from the 3 port. The 3 port only does something when heating is selected.
 
Thanks guys. Y Plan system. Going back tomorrow. Planning rocks yeh
 
You're mid position actuator is goosed. You could change just the syncron motor, but I usually change the complete head.
 
Yes thanks. I just changed it and works fine. I just didn't know that the 3 way valve signals the boiler to fire up in central heating mode. Need to do the honeywell course asap. Thanks again for the help gentlemen
 
Status
Not open for further replies.

Similar plumbing topics

I don’t know your boiler but would expect it...
Replies
3
Views
685
I don't believe moving the manual lever over...
Replies
5
Views
511
S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
131
S
M
Hello, We’ve recently moved into a fairly old...
Replies
0
Views
597
MartinPod81
M
Back
Top