Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Problem with thermostat in the Central Heating Forum area at Plumbers Forums

Messages
11
So I have a combi, my thermostat is Honeywell dt90e. Wanted to change thermostat to a programmable so bought a 2 wire programmable stat when wired In. The stat is calling for heat but boiler won't fire. I took stat off and connected a wago to both wires and the boiler fires straight away. Has anyone had this before or anyone know what's wrong. Thanks
 
Danfoss has a battery, mains and rf version of this. Can’t seem to find flowmasta version. Are you able to provide photos of wiring?
 
Last edited by a moderator:
because all it is , is a switch so live and switched live ***************

Best you get somebody with knowledge involved .
This
because all it is , is a switch so live and switched live ***************

Best you get somebody with knowledge involved .
Okay glad we cleared that up I have basic knowledge in it, still can't figure why boiler won't fire, because It works when I connect with a wago but not when wired to stay and there's only 2 ports on the stat
 
This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.
 
This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.

This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.
Thank you Timmy D will try that in next few days
edited that for you
No need for that , I understand need a course on it don't do much electrics
 

Similar plumbing topics

Sounds more like the heating zone valve isn’t...
Replies
5
Views
1K
Deleted member 120897
D
Hi, I am trying to link a Hive heating & hot...
Replies
0
Views
605
A
I have the exact same issue so keen to know if...
Replies
1
Views
400
Nicholas
N
I don’t know which version will be which, from...
Replies
3
Views
1K
Deleted member 120897
D
Back
Top