Had a problem with CH running continuously which I traced to a stuck two post valve (S plan system). That solved the issue but then I noticed the hot water is also on continously even if switched off at the progammer and irrespective of tank thermostat setting. With system powered off the 2 port valve closed completely. But swapped the HW and CH actuators over as a test and the HW still on continuously. Foolishly assumed probable tank thermostat issue (as the knob been broken off a while ago). Changed the tank thermostat and still HW on constinuously. I am presuming that the old Scottish Gas UP1 programmer is faulty but before I get a replacement thought would ask here. There is a frostat on the system but presumably that would not hold the HW port open if its faulty?