Good idea. Would the flow restrictor not be a manufacturers part?
Just to confirm an electric shower?
These babies have a fixed heat output on the coil. They rely on restricting flow to lower volumes to heat the water up to higher temperatures.
thus the "PRV" in this instance is the DIAL on the front of the unit indicating temperature, turn colder for more volume less heat and the other way for less volume more heat
It's down to the equation phi (pronounced fie) = MCP delta T
Phi = the rating of the coil in kw
M = mass flow rate of water
CP = specific heat capacity of water
delta T = the amount that the temperature of water is raised
8.5kw/ 4.2 x (40-5)
So to raise the water from 5 degC to 40 degC with an 8.5kw coil the flow rate will be 0.05l/s or 3.46 l/min
with a 9.5 coil flow rate will be 0.06 or 3.88l/min
The dial on the shower changes the volume flow rate, so that's your method of reducing volume to increase temp
Hope this helps