Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Pump not working on central heating in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
Messages
23
I have an open vented system with an oil fired boiler. The zone valve opens for the central heating, boiler fires but pump not working. Have checked inside of pump and the spindle turns freely. I'm thinking elecrical issue. Would changing pump head solve the problem. Thank you in advance for any replies.
 
Power to the pump ??
 
Check power to pump,
if yes, then try turning speed up, otherwise new pump.
What brand and type is it?
The modern pumps are full of electronics and this causes failures
 
If it's an older pump you'll be very lucky to get a new head, it'll be a new pump.
 
Its a grundfos 15-60. Not sure if there's power to the pump but its wired via a wiring box which is providing power to the boiler and zone valve. Have tried the pump on all 3 settings.
 
You need to prove there's power going to the pump first before doing anything tbh
 
Assuming you have power to the pump , if you just want to change the pump head, try to locate a Ravenheat non ERP pump head , it is a grunfoss with a Ravenheat badge .
 
Changed the pump head. All worked fine, rads getting hot, then about an hour later, rads cooling down, pump still working, room stat at max. Any ideas gentlemen.
 
Always fit the pump with the arrow facing the way the original one. The head can be removed and turned so better position for wiring.
 
What boiler do you have? Did you isolate pump via the pump valves or drain the system? Does the pump sound noisey even though the impeller is spinning (if pumps airlocked the sound reminds of the TIE fighters from Starwars :oops:)
 
I think there might be a blockage somewhere. Pipes hot from pump down past 2 port valve towards boiler but return pipe from boiler is cold
 
What boiler do you have? Did you isolate pump via the pump valves or drain the system? Does the pump sound noisey even though the impeller is spinning (if pumps airlocked the sound reminds of the TIE fighters from Starwars :oops:)
Oil fired boiler. I isolated the pump at the valves, changed the head only. Opened valves, bled all rads and the pump. All was fine for about an hour, then i noticed rads were getting cold. Its not the roomstat, ive bypassed that for now.
 
Is the feed blocked? And now the boiler is overheating and going to lockout?
 
Shut all upstairs rads, forced heat downstairs, then one by one opened the upstairs again, seems to have worked. will find out in the morning if they all get hot
 
Status
Not open for further replies.

Similar plumbing topics

Sometimes the connection point of the cylinder...
Replies
3
Views
549
L
Replies
2
Views
2K
  • Sticky
I have a weird intermittent problem where my...
Replies
8
Views
1K
Replies
8
Views
770
    • Like
Alpha 2/3 manual. Shows variant with air...
Replies
8
Views
1K
Back
Top