Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Pump or stat in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
62
Hi can anyone please help with a control issue I'm not sure about. Old system no motorized valves or wall stat, just a pipe stat at hotpress. 1 circulating pump for oil boiler and fire. Boiler fires up NP but only for 5 to 10 mins so I thought pump. Householder checked for vibration when boiler turned on, no vibration so thought def pump. Now he says it is vibrating and a little heat in rads since he lit the fire. Boiler still won't keep firing unless u turn boiler stat up. I'm now thinking dodgy boiler stat although its not going onto the high limit and tripping out. Any ideas and thanks in advance.
 
One pump for the oil boiler and fire??? That can't be right, unless the system is a DIY bodge.
I would still say it could be circulating pump. It could be vibrating but not pumping.
Check directly the pipes at the oil boiler temperature first to see if hot.
 
Thanks best, I wud personally like to fix this if I can as the guys father did me a favour with my car before. The old woman who did live in the house for 70 years says def only 1 pump. If the time clock powers the pump when boiler is running, what powers the pump when the boiler is off and the fire is only lit. Is there a sensor from the back boiler. I've no idea only oftec 101 not a plumber.
 
This sounds like a DIY installation?

I would recommend you get a heating engineer to look it over for you to rule out any lurking dangers
 
Definitely sounds DIY. It might be done in a stupid way with primary flow & return from
fire also linked to rad circuit and maybe some upstairs rads are working on gravity.
It is the fire side I would be worried about as it is uncontrolled.
Tell the owner not to light the fire until a heating engineer checks the system and gives advice on any issues. The pump, if it is definitely doing the oil boiler could be replaced to test
 
Thanks for all the input, safety first. While I service, repair oil boilers , replace circulating pumps , motorized valves etc I'm not a plumber so don't get involved. I have done oftec 101 and serviced and repaired quite a lot in the last 11 years. His plumber friend coming out tonight, I still think its pump, its fitted so the bearings won't get lubricated. No pump at boiler , just a pump near the fire and the elderly couple who owned the house insist 1 pump for both oil and back boiler.
 
Status
Not open for further replies.

Similar plumbing topics

I once had a similar experience with my old...
Replies
6
Views
857
Several people told me it would be an Airlock...
Replies
4
Views
697
I would agree, but only if the high stat were...
Replies
4
Views
1K
Replies
8
Views
770
All sorted now and running better than ever...
Replies
3
Views
1K
Back
Top