Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Pump overrun causes loud bang in the Central Heating Forum area at Plumbers Forums

Messages
4
Hello,
I am not a plumber, but I have done some DIY in the past, so I have some experience. Following a new boiler install by a professional about a year ago, there remains an issue when the pump overrun initiates. The boiler is a Worcester Ri compact installed downstairs. the pump is installed above it and feeds out to two Drayton 2 port valves, one for C/H one for H/W. Between the pump and the valves is a tee with a divertor to provide a by-pass during overrun. this works fine when the C/H closes down, but when the H/W closes down there is a loud thump as that valve closes against the pump flow, even with the divertor set to its lowest pressure. The H/W tank is about 8 or 9 meters away, upstairs and the pipes (28mm) are laid between the upstairs joists with minimal fixing (now difficult to access).
It is as if the Drayton valve is being forced closed suddenly by the pressure from the pump, but this doesn't happen with the C/H side. It doesn't happen when the H/W closes but the C/H is still open, only when the H/W on its own is running. The pump is running at its lowest speed. I have tried to eliminate airlocks by putting the pump up to top speed, then back down.
Has anyone else experienced this issue? (Cant find it mentioned anywhere on Google). Could the valve be faulty? It is fitted the right way round according to Drayton installation booklet.
HELP !!!
 
Hello,
I am not a plumber, but I have done some DIY in the past, so I have some experience. Following a new boiler install by a professional about a year ago, there remains an issue when the pump overrun initiates. The boiler is a Worcester Ri compact installed downstairs. the pump is installed above it and feeds out to two Drayton 2 port valves, one for C/H one for H/W. Between the pump and the valves is a tee with a divertor to provide a by-pass during overrun. this works fine when the C/H closes down, but when the H/W closes down there is a loud thump as that valve closes against the pump flow, even with the divertor set to its lowest pressure. The H/W tank is about 8 or 9 meters away, upstairs and the pipes (28mm) are laid between the upstairs joists with minimal fixing (now difficult to access).
It is as if the Drayton valve is being forced closed suddenly by the pressure from the pump, but this doesn't happen with the C/H side. It doesn't happen when the H/W closes but the C/H is still open, only when the H/W on its own is running. The pump is running at its lowest speed. I have tried to eliminate airlocks by putting the pump up to top speed, then back down.
Has anyone else experienced this issue? (Cant find it mentioned anywhere on Google). Could the valve be faulty? It is fitted the right way round according to Drayton installation booklet.
HELP !!!
it is being forced shut by the pump you are correct, try a new valve
 
it is being forced shut by the pump you are correct, try a new valve

Thanks for your comment, partly right. I decided to e-mail Drayton at the same time as posting this query. It seems the valve is upside down. The instructions say the flow should be "from A to B", so my assessment was based on the A and B on the actuator casing next to the manual lever, but Drayton say that the underside of the brass valve body is marked A and B, and they are the opposite to the markings on the actuator - hence the confusion. Hopefully, when my plumber comes and changes round the valve the thumping will have disappeared. Anyone using Drayton valves (with the detachable actuator), please note !
 

Similar plumbing topics

    • Like
Alpha 2/3 manual. Shows variant with air...
Replies
8
Views
1K
Yep, that's what I meant (as per attached...
Replies
7
Views
1K
    • Like
From this post, I think you’ve got a good...
2
Replies
47
Views
6K
D
Ah it's all sealed and can't get in to see the...
Replies
7
Views
1K
I just repeated this test. This time I got a...
Replies
6
Views
2K
Back
Top