Hi, im new here, im currently working towards my acs. Ive been practicing my purge calculations, ive been fine with them, but when it comes to checking the volume pass through whilst purging i need some clarification.
ok here goes
meter purge volume is 5 times badge capacity 5 x 0.071 = 0.355ft or 4 sections of the test dial.
so i have done my purge calculations and end up with 0.023
i understand i have to purge and ignite as its over 0.02
so how do i measure 0.023 on the dial?
This is what i think it is, and need this confirmed or guided towards the correct way please..
0.355ft is 0.01 in metric right? and thats 4 sections of the test dial,
so 0.01 divided by 4 = 0.0025 so each section of the dial is 0.0025?
0.023 divided by 0.0025 = 9.2
so i have to purge 9.2 sections of the test dial whilst applying ignition in order to light the appliance and get a good flame.
appriciate your time and help