eddiebrown424

looked at an install today and the pressurised cylinder cupboard ws completed in push fit. The tundish hadnt been conected yet but wht are peoples views on it. i personally only use copper but am told plastic is ok.

Eddie
 
thanks markfxy. Your right looks awful cant be a lot cheaper with all the bulky fittings either.

Eddie
 
Depends on what make of pushfit / plastic pipe. Wont be rated for temp/pressure unvented cylinder gives. Saw a few on sites ( was sent to fix) and a certain manufacturers pipe was used but at the temp stored and pressure it can build upto ,the fittings blew off. Was sent to fit copper to underfloor. And also fit copper for blow offs.
(ps this was years ago )
 