Hi,
combi boiler in the house 7 Bar from mains I have installed a prv to get pressure between 3-4 Bar. Is that correct?
 
Combi boilers have a pressure release valve set at 3 bar, so its best to fill the system at about 1 bar.
 
check on your boiler manual spec,
no bernie, the heating is not mains pressure its captive at 1-2bar.
generally 3bar cold mains to hot water sounds generall ok but a bit high depending on spec.
 
Redshaw he sounds as though he is going to fill the combi heating system although he doesn't say as much. If he charges it anywhere over about 1 bar it stands a chance of blowing off.

His water supply outside of the heating can be 3 bar, I suppose providing it makes no noise or causes errosion through excessive flow rates.

He should though as you say chec his boiler specs
 
Hi,
combi boiler in the house 7 Bar from mains I have installed a prv to get pressure between 3-4 Bar. Is that correct?
3-4 bar is fine most combis are rated at max preasure for inlet 10 bar but that would be noisey and cause wear
 
Thanks everybody. 7 Bar was too much I fitted PRV at 4 Bar and boiler and taps are fine.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
The flow is upwards through the PRV, it looks...
Replies
10
Views
481
  • Question
How high is the hill 40m as that will add 4...
Replies
2
Views
503
it is brand new ( 6 months old ) Worcester gas...
Replies
2
Views
742
losing pressure
L
You might have a EV (expansion vessel)...
Replies
7
Views
627
They don’t have a expansion relief eg prv is...
Replies
2
Views
717
Back
Top