Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss radiator balancing in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
187
Hi chaps,

It's the usual scenario.... 9 out of 10 rads all heating fine / the one which is not reaching the same temp as the others is in an upstairs bedroom. I have just spent most of today trying to get it to heat up but without much success. Some of the other upstairs rads have TRV's fitted on the return side - would this make any difference when trying to balance the system? or does it not matter and you just close or open the flow valve as you would a lockshield?

cheers

dave
 
most new trv are bi directional they work either on flow or return.
have you tried shutting all the other rads down to see if its a partial air lock ?
forcing all the flow through just that one rad should clear it if its an airlock or a bit of sludge restricting the flow
 
Hi Maul - yep - have closed all other rads down and sure this one heats up great. Thing is as soon as I open up the others it's temp drops. So definitely a balancing problem
 
It sounds like you need to balance the system, the radiators that are hottest can be turned down,this will push the heat to the problem radiator. Take off the cap on the lockshield valve and turn the spindle clockwise to close it,try a couple of turns to start with.You have to keep checking the radiators until they all "balance" out!
 
Full system powerfush would not go a miss should have a differance of 20 degrees between flow & return when balancing
 
... should have a difference of 20 degrees between flow & return when balancing
Not necessarily true. Some boiler work with an 11 degree difference. If you have a 20 degree difference across your radiators their output will be reduced by about 15%.
 
Status
Not open for further replies.

Similar plumbing topics

Since it became normal for trv's to be bi...
Replies
1
Views
582
You seem to have got it sorted, but for future...
Replies
7
Views
944
O
Have you tried waggling the pin on the trv...
Replies
1
Views
909
  • Question
Rather than open up all the lockshields and...
Replies
3
Views
1K
Replies
0
Views
448
Back
Top