Hi all
doing a complete refurb in an 8 bed house at the moment. The job has been specified and drawn up by a consultant.
ive checked today the outputs for a couple of rooms and don't get anywhere near his outputs!
example. Master bedroom 6.5 m x 5m. 2.6m high. Window (1.2x3.5m) 2 outside walls, heated above and below. New quality double glazing and the outside walls are 300cavity, with 100mm of exterior insulation. It's been done to 2010 building regs. It's a gas boiler system with weather comp.
between a mears calculator, and a couple of apps (Mr combi & btu calculator) I get between 2050w-2450w. The consultant has 1250w!
Can anyone get near that with other calculations?
dont really want to question the consultant, without getting facts right.
Cheers guys