Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Radiators only luke warm if hot water is on in the Central Heating Forum area at Plumbers Forums

Messages
2
Radiators are only getting luke warm if hot water is on but boiling hot if hot water is turned off. It’s either hot water, warm radiators or warm radiators hot water cavy seem to enjoy both anymore. We had the system professionally power flushed in Feb this year so what could the problem be. Thank you.
 
I’m guessing you have a hot water cylinder and an s-plan or y-plan setup? If not, can you tell us what system you have?

I’m also guessing you mean hot water warm rads, or hot rads warm water?
 
I’m guessing you have a hot water cylinder and an s-plan or y-plan setup? If not, can you tell us what system you have?

I’m also guessing you mean hot water warm rads, or hot rads warm water?
Good morning and thank you for your speedy response.

We have an emersion heater upstairs in the airing cupboard and a cold water tank in the loft. Downstairs we have a gas boiler (not a combi boiler) for the central heating and hot water.

As for the s-plan / y-plan question I’m so sorry but I haven’t a clue what that is! How do I find out please?

Thanks again. xxc
 
An S-plan is x2 motorised valves independently controlling heating and hot water, or both on together. A Y-plan is one motorised valve, also known as 3 port mid position valve, which still does the same, just one valve as opposed to 2 and usually a higher failure rate. The way to find this out is to go to your airing cupboard and just after the circulating pump (usually) should be the valve(s). If you’re unclear still, take and upload a photo of airing cupboard and we’ll be able to tell you.
 

Similar plumbing topics

1/4 turn black knob on both. open bleed screw...
Replies
7
Views
833
O
Have you tried waggling the pin on the trv...
Replies
1
Views
909
G
Could be one of a number. Need to know what...
Replies
1
Views
668
M
Teed off of 10mm feeds from original rad?
Replies
2
Views
792
Back
Top