Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Random occurrences of no hot water in the Gas Engineers Forum area at Plumbers Forums

Messages
16
Hi all,

I posted a few months ago about a 'no hot water' problem, and it turned out that it was a diverter valve problem.

But still, from time to time, not too frequently fortunately, we have only lukewarm/cold water in our taps/showers. What could be the problem?

- sometimes, the trick to have hot water in the shower is to open the tap and run the water in the adjacent sink. It 'forces' the water in the shower to come hot. It is just a bit wasteful to do that...
- sometimes this trick doesnt work.

It is a bit surprising as the programmer says that the hot water is on. Also, I can see that when it happens, the boiler (Vaillant home system 15) displays a temperature of 40-45 degrees. So not hot enough.

Eventually, the hot water comes back, maybe an hour later. So there is a delay. Again, it is very random and fortunately not too frequent, but still a bit annoying.

Any clue? Thanks in advance for your thoughts.
 
I’m a little confused by this, as you mention a diverter valve and system boiler. If you have a system boiler, the chances are there’s a control fault, so possible 2/3 port valve issue.
 
I’m a little confused by this, as you mention a diverter valve and system boiler. If you have a system boiler, the chances are there’s a control fault, so possible 2/3 port valve issue.
well, I was a little confused too when the engineers fixed the thing. He really changed a 'diverter valve' as he said, and we do have a 'system' boiler.
 
I have attached some pictures. Again, I'm no expert, but I'd like to understand my system. Thanks!
 

Attachments

  • cyl1.JPG
    cyl1.JPG
    217.8 KB · Views: 9
  • cyl2.JPG
    cyl2.JPG
    225.9 KB · Views: 9
  • cyl3.JPG
    cyl3.JPG
    260.9 KB · Views: 8
You have an unvented hot water cylinder, so likely a system boiler, and an s plan plus. Valve looks like Honeywell, so if it’s been replaced it’s unlikely it’s failed, although not impossible.
 
You have an unvented hot water cylinder, so likely a system boiler, and an s plan plus. Valve looks like Honeywell, so if it’s been replaced it’s unlikely it’s failed, although not impossible.
The OP mentioned that he has a "Vailant home system 15" boiler, which IIRC has a 3-position internal diverter valve that can be CH only, both CH and HW, and HW only.
 

Similar plumbing topics

  • Locked
Closed time to get a gas safe engineer out
Replies
7
Views
1K
Check the continuity of the flue with your...
Replies
3
Views
2K
M
Hello, We’ve recently moved into a fairly old...
Replies
0
Views
587
MartinPod81
M
Are you Gas Safe Registered? If not please...
Replies
2
Views
536
  • Question
You've fecked up, it's not the way to do it...
Replies
18
Views
1K
Back
Top