Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Relocate mains water supply in the Bathroom Advice area at Plumbers Forums

Messages
9
Evening all,

Fresh to the forum so hello first!

Well right to it. I am currently mid flow with a new kitchen design but need to establish something before we go any further. My mains water supply comes in directly under where the sink is currently located as normal. But if tou check the photo out i want to do away with the units under the window altogether and relocate the sink to the recess to the right. So in doing this the mains water pipe will be left exposed and in completely the wrong place. Ive also attached a picture from the new design so it hopefuly makes a bit more sense what im trying to achieve.

I need to know two things really. 1) can it be relocated to under the new sink location? And 2) how much and who can do it!!

Many thanks in advance boys and girls.

Cheers

Matt
 

Attachments

  • 1455135233445517889303.jpg
    1455135233445517889303.jpg
    92.2 KB · Views: 55
  • 14551359467671471449024.jpg
    14551359467671471449024.jpg
    108.9 KB · Views: 44
you will have to dig it up put a coupling on and run it under the screed easy enough for a plumber but could be a bit beyond basic diy

but that gets alot harder if its steel
 
Joints in screed are best avoided. If location of pipe can be established outside building, then drill and sleeve for new entry to required location. Usually less than two hours work. Minimal disturbance to existing flooring.
 
Joints in screed are best avoided. If location of pipe can be established outside building, then drill and sleeve for new entry to required location. Usually less than two hours work. Minimal disturbance to existing flooring.

how do you come up with that it would take, two hours to dig the hole outside and its still got to come up through a concrete floor i suspect alll your plumbing knowledge comes from books
 
Last edited:
The two hours is for drilling and sleeving from inside to outside. First mistake most make is to start core too close to wall. Proceed as follows:-
With centre of hole approx. 300mm off wall, core through screed insulation and oversite concrete with 100mm core bit. As core starts to bite into screed angle drill so direction of core is towards wall.
Once through concrete, next problem is loose stone below. Overcome this with straight crowbar and plastic sleeve. Bar driven to wall/footing and wriggled to enlarge hole. Plastic pipe, 50mm diameter, slid down bar to sleeve hole. Hole in oversite concrete used as fulcrum to assist process.
1 metre,25mm, SDS bit now used to drill through wall/footing.
Enlarge hole with 38mm core bit and extensions. Do not be tempted to use smaller size as shoulder of core will not pass through hole.
I accept that in east London / Isle of Dogs many houses are on pile and beam foundations and cores should not be made through RC ground beams, but for the majority of properties elsewhere, on strip or trench fill foundations, the procedure works and 2 hrs is more than adequate.
 
The two hours is for drilling and sleeving from inside to outside. First mistake most make is to start core too close to wall. Proceed as follows:-
With centre of hole approx. 300mm off wall, core through screed insulation and oversite concrete with 100mm core bit. As core starts to bite into screed angle drill so direction of core is towards wall.
Once through concrete, next problem is loose stone below. Overcome this with straight crowbar and plastic sleeve. Bar driven to wall/footing and wriggled to enlarge hole. Plastic pipe, 50mm diameter, slid down bar to sleeve hole. Hole in oversite concrete used as fulcrum to assist process.
1 metre,25mm, SDS bit now used to drill through wall/footing.
Enlarge hole with 38mm core bit and extensions. Do not be tempted to use smaller size as shoulder of core will not pass through hole.
I accept that in east London / Isle of Dogs many houses are on pile and beam foundations and cores should not be made through RC ground beams, but for the majority of properties elsewhere, on strip or trench fill foundations, the procedure works and 2 hrs is more than adequate.
Me thinks that lot didn't come out of a plumbing book, what do you think steve ? :builder:

Just a tip to anyone brave enough to have a go at that - double check that you know where all the other utilities are first !! You really wouldn't want to locate your incoming electrical supply with a core bit.
 
Last edited:

Similar plumbing topics

  • Question
Well done, BUT, does it work and then does it...
Replies
8
Views
873
  • Question
Yes potentially your existing pipework could...
Replies
6
Views
951
  • Question
have you had a plumber have a go with the...
Replies
4
Views
896
  • Question
Probably all off one main hence your problem...
Replies
3
Views
801
  • Question
Ah -- couldn't see "attach files" on my phone...
Replies
4
Views
752
Back
Top