Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Repeated air/hydrogen forming in closed heating system? in the Air Sourced Heat Pumps area at Plumbers Forums

Messages
1
Would love some advice please:

I had 4 radiators replaced in September as part of a kitchen refit. This included new copper piperwork behind the walls where the Rads are placed. The system wasn’t flushed or anything, just installed and the plumber left.

A few weeks later we noticed that our two uppermost radiators (not new ones) weren’t heating fully.

We spoke to a Gas Engineer who assessed the boiler - which was fine - and said that as we have a Closed Heating System we either have:

a) hydrogen forming from the flux because the plumber who fitted them didn’t flush the system it add inhibitors or

b) we have a leak somewhere.

We have no visible signs for leaks so what he did was add System Cleaner and left it a week with us having the heating on a lot to circulate it.
He came back, ran a simple flush and added in a Miracle Seal & Corrosion Inhibitor.

However now, 3 weeks later, the same two radiators are not fully heating up again.

The boiler pressure, which I’ve been monitoring every other day, remains the same. Worth noting that I did hear “bubbles” passing through other radiators recently. And we also had a new air vent “thing” installed to replace a faulty one (see photo) - could that be sucking in air???

It’s an ideal logic boiler that manages both hot water and central heating with an unvented megaflo water tank

Any ideas???
940C3F36-E870-492C-8F00-0EC3A2A7AF71.jpeg
 
Last edited:
Fresh copper in a heating system will evolve hydrogen at a gradually reducing rate for, typically, about six months. This is a side effect of the 'passivating layer' forming.

I'd just bleed the affected radiator(s) and top up to restore the system pressure if necessary. Expect to need to do this several times at lengthening intervals for about six months.

A correctly place automatic air vent can avoid the need to bleed radiator(s) manually but you may still need to top up with water a couple of times to replace the water that has been converted to hydrogen and copper oxide by the above process.
 

Similar plumbing topics

Local water is close to pH 7. A professional...
Replies
4
Views
1K
  • Question
we have 2 separate valves and they both open...
Replies
2
Views
881
S
  • Question
Hi guys, we moved into a place last Dec with...
Replies
0
Views
958
Sam Grocock
S
Pin hole leak on suction side of pump.
Replies
1
Views
465
  • Question
Only other items that may cause noise are the...
Replies
13
Views
2K
Back
Top