Hi Guys,
just wanted to get some advice on the wiring of the new MC6 thermostat?
I have attached a picture of what I am replacing and the wiring diagram of the new Thermostat. Please also see recorded voltage readings I have taken.
Current Honeywell Stat :=
1= 230v always (Red)
4= 230v
3= 0 (Yellow)
2= 0 (Blue)
When thermostat switched on
4=0
3=230v (Yellow)
2=0 (Blue)
So based on this the new wiring diagram would be?
Red = L ( Live)
Blue = N (Neutral)
Yellow = No ( Switched Live)
Please note I am not using it to control Hot water.
Do I need to jumper between L (Live) and COM?
Thanks for any advice and if you need any more information?
Thanks.