Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Replacing broken internal expansion vessel on a worcestor 24 cdi boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
T

thecalvers

Fitting an external expansion vessel to my central heating pipework seems straightforward but I don't know what 'tidying up' :hammer: will need doing with the vessel in the boiler

does the vessel inside the boiler need decommissioning or adjusting somehow?

Thank you for your input.

thecalvers
 
no just leave it mate. as long as the new one is working then the old one can just be left in.
 
A plastic cap on schrader may not go a miss , if its missing.
in case it drips !

( By some one GSR , next time its serviced ! )
 
Last edited:
Agree with dust cap. Sometimes a schrader can pass when diaphragm is perished.

A pea sized amount of jet blue in schrader and cap on. Label to say u/s but still connected
 
Agree with dust cap. Sometimes a schrader can pass when diaphragm is perished.

A pea sized amount of jet blue in schrader and cap on. Label to say u/s but still connected


Thanks, that's very helpful. I'll just fit a dust cap, label the EV and fit one externally. I assume that fitting one the same size as the internal one is the said thing to do.. if I add a rad to the system will the expansion vessel have to be changed again? Should I upsize to a bigger EV just in case I hae extra rads fitted?

Thanks guys,

thecalvers.
 
More is best , manuf often under size original to save pennies which is why they die !

Long pipe runs soon mess up what is normal .
 
the new expansion vessel will come with a pre-set charge that is probably higher than you will require.
check your boiler installation manual for the required vessel charge pressure ( likely .7 bar )
check this before fitting/pressurising the system
 
Last edited:
you can buy a electronic pressure gauge from screw fix for around £7. they are very handy piece of kit. the best balance is to have the expansion vessel between .1 and .2 under the system charge when filled cold. with the expansion vessell being set slightly less than the system it expands into to vessell easier. example vessell charge 1 bar system charge 1.1/ 1.2 bar
 
Status
Not open for further replies.

Similar plumbing topics

ah i see what you mean, just need something...