Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Replacing old Ideal Mexico RS50 Boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
V

vaultsman

Good Evening all,

1st time here...and no expert!...so please be gentle!

I'm looking to replace an old Ideal Mexico RS50 regular boiler with a system boiler. The RGI (who works mainly in industrial/commercial) who'd do the work likes Main boilers...but also Worcester. He's an ex-neighbour of mine.

According to the info plate on the old boiler, the RS50 is rated at 14.7 kW max, but the smallest SEDBUK A Main system boiler (ECO) I can see is rated 24 kW. Are these boilers modulating? Or is 24 kW much too oversized?

The property is a 1930's 2-bed semi and, from a quick calculation at Replacement Boiler Size Calculator , a 15 kW boiler seems about right.

I'm (probably) tending towards a Worcester 15i or 18i instead.

Any help and guidance gratefully received!
 
Vaillant eco boilers can be range rated to suit your needs. All boilers modulate now
 
Thanks AB,

Does that mean that Main boilers can't be range rated? And does range rating affect efficiency significantly?
 
Dont know about Main's. But Vaillants can defo be altered 1Kw at a time. Good boilers too
 
All A rated boilers will modulate down to suit the load (some lower than others) so there is not really a need to range rate anymore.
 
Thanks tamz,

So there's generally not really an efficiency penalty in oversizing?
 
dont forget you need to allow for the pipework + cylinder in you calc. I tend to go with 5000btu+15000for a standard cylinder on top of the heat requirements.
 
Thanks tamz,

So there's generally not really an efficiency penalty in oversizing?

Not really as long as you don't go totally over the top. Check the boiler MI's and it will tell you the minimum rating. A worcs 18i for eg will modulate down to 5.54kw and the 24 down to 7.38. Remember the load will decrease as the system heats up and trv's start closing.

The worcester Ri boilers are regular boilers so you would need an external expansion vessel and pump. Their system boilers are i system.
 
Last edited by a moderator:
Not really as long as you don't go totally over the top. Check the boiler MI's and it will tell you the minimum rating. A worcs 18i for eg will modulate down to 5.54kw and the 24 down to 7.38. Remember the load will decrease as the system heats up and trv's start closing.

The worcester Ri boilers are regular boilers so you would need an external expansion vessel and pump. Their system boilers are i system.

Thanks again tamz,

The spec on the Main 24 Eco gives heat outputs (condensing) as 8.37 kW min and 26.95 kW max...so I'm thinking that minimum figure could be a tad on the high side as the load drops?

If I do go for the Worcester, yes, I'd probably plump for the 18i.

Cheers,
 
Status
Not open for further replies.

Similar plumbing topics

Thanks to @ShaunCorbs and @cjg for the helpful...
Replies
7
Views
804
There must be many installations that are in...
Replies
7
Views
921
hello, old post but what did you go with in...
Replies
11
Views
7K
Deleted member 131795
D
Is the prv dripping outside ?
2 3 4 5 6 7
Replies
174
Views
14K
Back
Top