Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Repressurise white expansion vessel in the UK Plumbers Forums area at Plumbers Forums

Jennie

Gas Engineer
Messages
283
Hi all,
I've got my G3 card. First time I've attempted to re-pressurise the white, expansion vessel above an unvented cylinder.
I first turned the water off, ran the taps to relieve the pressure. The vessel (it was flat). I managed to pump it up to 1.2bar with no issues. But then it was extremely hard to pump.
A plumber before me had the same issue. He'd also removed the vessel to do this.
My question: is it physically possibly to get to 3bar with a foot pump? Or should I use an electric tyre pump (such as is used on car tyres)?
Regardless, the customer needs a new vessel as it didn't hold the charge. But I'd be interested to know how you'd all repressurise it.
Jennie
 
Sounds like the vessel has been over expanded due to it not having air in

time for a new vessel then

but to your question yes it’s doable around 5mins normally to do one
 
Another +1 for the stirrup pump with long hose. Makes it possible to charge vessels in all kinds of locations whilst keeping the stirrup pump on the floor. With my old pump sometimes I had to put the base of it against the wall in an airing cupboard and work the pump horizontally which is no fun at all on the bigger vessels.
 
leave hot tap open whilst you inflate it.

Whilst OP was aware of this being necessary, I am amazed at the number of plumbers who do not know this or didn't remember to do it at least. If you think about what function the vessel is performing and how it is constructed it should be pretty obvious that you need to charge with zero pressure on the wet side but so many don't do this and end up undercharging the vessel.
 
Whilst OP was aware of this being necessary, I am amazed at the number of plumbers who do not know this or didn't remember to do it at least. If you think about what function the vessel is performing and how it is constructed it should be pretty obvious that you need to charge with zero pressure on the wet side but so many don't do this and end up undercharging the vessel.

Yes many still get it wrong and end up with a false reading.
 
OK, I have a similar problem here. I have cold water coming out of the overflow when boiler running. Nothing comes out the tundish. I spoke to a friendly plumber outside Screwfix and he suggested I open the hot taps and try pumping up the vessel. However it is not holding any pressure and when I turn the water back it it sounds like the vessel just fills up with water. I am not a plumber but figure that the vessel must have some kind of diaphragm inside.

Would mine be comprised if I can not get it to pressurize?
Can I change it my self (looks straight forward) or do I need a G3 card?
They come pre pressurized right?
 