I've been asked to look at a system that has had some work done by a previous engineer. The boiler was suffering from flame-outs and the previous guy ended up replacing the oil pump. The boiler is still cutting out, and after checking the usual suspects, (oil pressure, water in tank, pump pressure, nozzle, etc) it looks like the solenoid valve isn't allowing sufficient oil at the nozzle. It sounds suspiciously like the previous symptoms, but this is apparently a brand new pump, so before I replace it, does anyone know the specification for the valve to check it's within bounds (spring force, actuation distance)? It's an RDB 1. Thanks