Hi guys, will be grateful for your advice. Riello rdb1 in Grant combi. When boiler has been switched off for several hours on start up burner cycles properly and boiler runs OK. Having reached operating temp with heating and hot water all fine, on demanding heat once again the fan motor runs but start cycle goes no further and there is no lock out after 12 secs, motor just keeps running. Isolate from mains and leave for several hours and starts OK again. Burner has new pump, control box and capacitor. Any thoughts? Thanks for your help
 