Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss rules for boilers in lofts in the Boilers area at Plumbers Forums

Status
Not open for further replies.

michael c

Plumbers Arms member
Plumber
Gas Engineer
Messages
609
Hi guys qouted for a boiler install today with desired location being in loft right infront of the hatch. I have paid for the regs but they arent working at minute can anyone tell me what the rules are around this? The loft is boarded its just the proximity to the hatch im concerned over but the only other option is a bedroom.

Thanks in advance
 
There are no specific rules or regs but common sense tells you it should be floored, at least from the hatch to the boiler, be well lit and a loft ladder fitted.
If it isn't the boiler manu's or anybody else in the future may refuse to go up to it on h&s grounds. Some might even want a handrail around the hatch.

Don't fit it up there if the customer is elderly.
 
No where else to put it mate looking at putting a rail around hatch the ladder needs to be removed but customers says they will replace (needs to change orientation). I just didnt know if the boarding, rails lighting etc was a recommendation or a reg.
Thanks mate
 
Thanks mate im taking out existing but hopefully new one will be fitted.
 
It very much depends on the attitude of whoever has to work on it or access it. Some wouldn't bat an eye but others, especially those employed by the bigger companies will refuse to go up if things are not right to their H&S standards..
 
This is taken from the Glow Worm web site

[h=2]What are the requirements for a loft installation?[/h]Boiler installations in roof spaces should comply with the following additional requirements:- • Enough vertical clearance should be provided to satisfy the static head requirements for an
regular heat only system
• Fixed flooring should be provided under and around the boiler for servicing, also from the
entry point in the loft
• A permanent means of access to the roof space should be provided e.g fixed, retractable loft ladder
• Fixed lighting should be provided
• A guard should be provided to prevent contact between stored articles and the appliance
• The exit from the roof space should be provided with a guard rail to prevent anyone falling
• Isolation of gas, water and electricity should be possible without entering the roof space

Most manufacturers will have similar requirements which will need to be adhered to.
 
my understanding is that light ladder and floor are building regs requirement, at least that is what buildings control told me to do when i converted my flats a while back
 
The only mention of requirements in the building regs is this passage from Part J

Access to combustion appliances
for maintenance
1.59

There should be a permanent means of
safe access to appliances for maintenance. For
appliances installed in roof-spaces, walkways
may be necessary for this purpose
 
Well that clarifies there has to be permanent loft ladder thanks guys. Not much space between boiler and hatch so will have to think how best to do it.
 
and being they quote safe access youll need lighting as its not safe to crawl around unlit attics
 
There is currently lighting, flooring, hand rail and ladder. Hand rail and ladder need to change orientation to allow install though
 
Im not covinced about the loft ladder, the way I read it there should be flooring to ensure safe access to maintain the boiler and a light. but i suppose the health and safety police frown on using a bannister and a pull up to get into the attic ;-)
 
As i said before it very much depends on the attitude of whoever deals with it in the future.

What about working on a CWSC. What "rules" are in place for fixing a ballcock or even jumping up to turn the water off. Gloves and goggles and disposable overalls and a map in case you get lost in fibreglass.
It is all a load of pysh!
 
Im in probation after going self employed so just trying to ensure i cant be picked up on it
 
AS others have ststed, lights, boarded and ladder.
Maybe a fitted toilet to stop people relieving themselves in the cwsc:D
 
basically its just common sense and nobody is gonna send you down if one of the above is not up to spec. i go to loads that aint done properly. so i tell the custy but nothing gets done and i dont like wasting my time so i end up doing the service anyway
 
BS 6798:2009
roof space installation
Point 5.3.8
among other things:
floor boarding
a fixed permanent light.
purpose design access - can be a loft ladder.
 
Going to make educated decision next time im back the existing ladder needs to come out but unsure if able to reorientate may just have to fit a condensate pump and place at other end of loft (not an ideal situation as entire loft boarded including roof and walls. With a large built in unit which didnt want to rip out.
 
I wouldnt worry about the loft ladder stick the boiler in the desired location and provide isolation on the first floor
 
Status
Not open for further replies.

Similar plumbing topics

Hi appreciate and thanks to all that replied...
Replies
11
Views
1K
Come on pal , you should have painted the...
2
Replies
27
Views
8K
Thank you for the detailed and considered...
Replies
14
Views
1K
I think a lot of us suspect your cylinder is...
Replies
12
Views
2K
I feel for you, it's a bad position to be in...
Replies
18
Views
2K
Back
Top