Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss sabre 29he combi boiler not working after removing radiator in the Boilers area at Plumbers Forums

Status
Not open for further replies.
D

derekg

Hi, just drained and removed 2 radiators from my living room so I can plaster my walls now my boiler is showing 0 bar and no hot water, can anyone give me any advise please.

Derek
 
you will need to re pressure the system what boiler / set up do you have combi or unvented cylinder?
 
Its a sabre 29he combi ,at the moment red light showing on boiler
 
you will see something like this below the boiler

28alrh2.jpg


to re fill turn both (there may only be one) valves so they are inline with the braided hose and you will see the gauge rise stop filling by turning the valve back to hosontal position when it reaches just over 1 Bar 1.2 ideal
 
All i did tonight was drained the water from the 2 radiators that i have in my living room, radiators still on the wall, still to cap the pipes, then the problem with the boiler.
 
All i did tonight was drained the water from the 2 radiators that i have in my living room, radiators still on the wall, still to cap the pipes, then the problem with the boiler.

yes doesn't take much to release the pressure out of the boiler, did your turn the valves off?
 
do i need to turn boiler off/on as its showing red light?

some you do some you dont but it should go out once you have a pressure of 1-1.2 bar on the dial
 
turned the valves off on the radiator

they might be passing so thats why your system pressure has dropped, you might have to cap the pipes for now and change the rad valves when you put the rad back on
 
trying to re pressure the system still showing 0 bar and a gurgling sound coming from the boiler
 
trying to re pressure the system still showing 0 bar and a gurgling sound coming from the boiler

yes keep going the gurgling sound is the air in the system you will have to bleed the rads afterwards
 
will i cap the pipes first before trying to re pressure the system or does it not matter and how long should it take to re pressure the system?
 
will i cap the pipes first before trying to re pressure the system or does it not matter and how long should it take to re pressure the system?

if you can cap the pipes first/ get new rad valve if you can as your ready drained down and you should see some movement in the needle within 3-5 mins
 
no probs will let you know how i get on thanks again for your help.
 
Status
Not open for further replies.

Similar plumbing topics

the op says no water in prv balloon so not prv...
Replies
7
Views
1K
A
Hi, I have a combi-boiler system and while I...
Replies
0
Views
399
Allan 1234
A
System boilers have a pressurised heating...
Replies
1
Views
273
R
Hi, The outlet of all my radiators are at...
Replies
0
Views
404
Renato
R
Back
Top