Hello
I'm only qualified 11 months in plumbing.
Its things like this where I'm lacking in experience :


I installed a Salamander pump & a Bristan mixer shower to a customers house.
They just had a bath only in their bathroom on the 2nd floor. (Existing Shower room on the ground floor - with a pump / mixer shower)

They wanted me to fit a mixer shower & a pump.
So, I Tee'd the hot & cold off the bath taps (22mm) & ran 22mm pipes to a Salamander pump. (RSP75)
(output to the shower was 15mm)

When the customer turns the shower on - nothing happens.
It can take 5 or 6 turns on & off before the pump kicks in - then it runs fine.
(When I installed it & tested it - it all work fine - started up immediately)

Its a 2 storey house + an attic above.
The CWSC is in the attic & the Hot Water Storage is on the same floor as the pump / bath (2nd floor)

Is this a flow problem ?
or should have I installed a negative head pump.

any help much appreciated.

Cheers
David
 
shouldn't really have teed into the bath feeds, shower pumps should always have their own dedicated feeds from the hot cylinder and cwst. also the pump should be situated at the base of the hot cylinder not under the bath.
 
Upvote 0
sounds like the shower feed supply is drawing very slightly to the kitchen when the hot supplies are being used there inhibiting the flow switch to be activated.
this will burn out the pump rotors and invalidate the warranty as in the m.i.

does the hot feed pipe fall into the pump or is the pump drawing the water?.
it worked when you installed it because you primed the shower!!
 
Upvote 0
Thanks for the input guys.

I fitted single check valves to the "exit" pipes to the shower (Hot & cold)
Surely this wouldnt affect it ?

I think I'll re-plumb it - by disconnecting the bath taps & run it straight to the shower.
If that cures it - I'll need to run new pipes from the tanks.

The Hot storage tank is only about 3 feet way in a cupboard (same level)

David
 
Upvote 0
Cheers Mike.
I'm going to replace the check valves with straight couplings.
Hopefully this might do it. - If not, I'll need to re-plumb it.
I'll keep u posted
Cheers
David
 
Upvote 0
SORTED !!

It was the check valves that was the problem.
They wouldnt even open when I blew through them.

I replaced them with 2 straight couplings.

I know now for future !
Thanks for all the input.

Cheers
David
 
Upvote 0

Similar plumbing topics

  • Question
Thanks for asking Lou. After taking 30+...
Replies
2
Views
589
  • Question
Hi SI......is the shower on the same floor as...
Replies
12
Views
366
  • Question
Yes mate we do 😉 12 years is good for a...
Replies
3
Views
1K
  • Question
This might be of interest...
Replies
1
Views
596
Back
Top