Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Salus IT500 Wireless Thermostat Wiring Help Needed in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
11
Hi All,
I need advice on which wires go where, i have a Drayton lifestyle programmer for hot water and central heating and I am trying to fit a Salus IT500 wireless thermostat. I need to know how to wire this up.
picture attached show current setup,

stat.PNG


PNZX6156 (1).jpeg


HUDW2394.jpeg
 
L to live
N to neutral
Link live to com
4 to ch no
3 to aux no
1 to aux nc

Hope this helps
 
When you turn the heating on does the port valve move at all

Also pump should come on if boiler comes on as there wired together
 
When you turn the heating on does the port valve move at all

Also pump should come on if boiler comes on as there wired together

  1. Hi Shaun,
    no, the port valve stays in the same position, no movement,

    boiler fired up and hot water working all ok, but the central heating will not fire up, its as if no signal or feed there.
 
hi shaun,
i have put the old set up back on until after xmas day,
if its all right when you, can i touch base with you then for some more help on this
 
Did you install both links like in your pic ?
 
Hi Shaun
I have just rewired as instructed, central heating working all ok, no concerns, but the hot water will not fire up, when I put the central heating on the valve go to the right and stays there even if I try and fire up the hot water, the only way I can get the valve to move back is if I disconnect the white wire. picture attached to the current wiring

IMG_0335.JPG
 
Is the cylinder stat holding it off ?? Eg upto temp ?
 
Is the cylinder stat holding it off ?? Eg upto temp ?

Hi Shaun,

could be, the tank is hot from this morning and I haven't used any water.

I will programme the app for hot water and central heating times and see if it works then.
central heating great, thanks for the quick reply, will let you know.

Shaun
 
Status
Not open for further replies.

Similar plumbing topics

Either will be fine also your salus will fit...
Replies
4
Views
1K
Keep the wc and use an eph combi pack 4 eg...
Replies
1
Views
517
Sounds more like the heating zone valve isn’t...
Replies
5
Views
1K
Deleted member 120897
D
That is true - however with Vaillant...
Replies
4
Views
848
Finally got an update from him. He cant do the...
Replies
2
Views
796
Back
Top