Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Sealed system grabbing air in the Air Sourced Heat Pumps area at Plumbers Forums

Matt0029

Gas Engineer
Messages
1,177
Any ideas why a sealed system with a combi could be grabbing air. The upstairs rads have air in and the system reads 3 bar cold. When the air is bleed out the system returns to 1 bar or less. It's an ideal instinct boiler basically a logic.
 
You sure it’s not hydrogen ?
 
I could bleed and test with a lighter? I wondered if you'd be anything to do with the expansion vessel. It's happened to quiet a few houses on this new build estate as said around 6 years all
If you can prove to have to have hydrogen in your system, you know its galvanic corrosion. Add some more inhibitor.

Incidently, I had a long chat with Hepworth technical (Hep2O) years ago about the virtues of barrier vs non barrier pipe (in relation to oxygen crossing it). And yes non barrier pipe does let a lot more oxygen across compared with barrier but its still nominal compared with the oxygen that gets into a system via radiator valve glands- apparently its the top crossing point by a country mile for oxygen ingress. Those cheap unglanded lockshields are a death sentence for your system. Volume house contractors often use cheapo valves . Id also be looking at that.

As a side issue ,after 6 years it would be normal to have to replace the expansion vessel in your boiler . They're only 10+ litres and subsequently have to work really hard in an 8+ radiator system . Its also a lot warmer in the boiler casing compared to an external one (and plumbers tend to oversize external ones because theyre relatively cheap ) and heat reduces the the life of the butyl rubber dramatically. External ones are barely warm to the touch during use
 
Strange though that its not lifting the PRV as the pressure is 3bar when cold which should mean that it had to be higher when the systen is/was hot?
Apparently non barrier piping can still absorb oxygen even in a pressurized system but one would think that rad valve glands would not inhale air except that some are under negative pressure.
I have a > 30 year old rad in a converted attic to bedroom with a open vented system (combined cold feed and vent), this rad allways runs with slight negative pressure but have never had any problems, I also think that at least some of the piping is non barrier.
 
If the expansion vessel is correctly charged and working okay then you'd need a lot of corrosion to evolve enough hydrogen to raise the pressure of the cold system to 3bar. It would take ages to bleed. (I suppose it's possible but, unless the system is an unusual combination of metals and a sacrificial anode needs replacing, it doesn't seem likely.)

I suspect you have a failed/failing expansion vessel. If this is the case, even a small amount of corrosion will jack up the cold-system pressure dramatically.

So, I'd investigate the EV first, also check the pH and inhibitor level in the system water. If the EV has been faulty, the PRV in the boiler will have been operating. The system seems to sit at 3bar when cold so it's probably reseating okay but I'd want to keep an eye on the outlet and pressure in normal operation to make sure it isn't passing.
 
I would add cleaner but also have a look at any towel rails sometimes they can cause bad corrosion if there cheap
 
Have you physically checked the pressure in the system ? it could just be a faulty gauge or partial blockage in the tube , I'd suggest and good hot flush then a chemical clean and mains water flush check then expansion vessel is charged to 0.7 -1 bar add a couple of litres of quality inhibitor before filling slowly and avoid trapping air in the system even fit manual air vents on high spots if necessary. Kop
 
Have you physically checked the pressure in the system ? it could just be a faulty gauge or partial blockage in the tube , I'd suggest and good hot flush then a chemical clean and mains water flush check then expansion vessel is charged to 0.7 -1 bar add a couple of litres of quality inhibitor before filling slowly and avoid trapping air in the system even fit manual air vents on high spots if necessary. Kop
I didn't no, I just bleed the gas/ hydrogen out. Which took the system back down to below one bar.
 
Hhmm was there a smell when vented did water come out? test the water there's many Kits available and we should really be doing it . I would say it needs a clean and possibly a new vessel you may possibly get away with not doing it ? , but if you're gonna be there a day why not do it and avoid another trip later your customer only has the one bill then and just gives a bit more peace of mind you've done the job best you can. Kop
 

Similar plumbing topics

  • Question
It could well be, the OP will soon hopefully...
2
Replies
35
Views
2K
  • Question
Red circles show my new AAVs and the manual...
Replies
17
Views
2K
  • Question
Before doing this, check the level in the cold...
Replies
9
Views
914
  • Question
It could be best to get him back to have a look
Replies
24
Views
2K
Back
Top