Hi,
Our sealed central heating system keeps losing pressure and we have to top it up very frequently. So in an attempt to work out whether it is the pipework at fault or the boiler I have done the following.
1. I connected a pressure gauge to one of the rads and pressurised the system to 3 bar. The 3 bar pressure did not hold and within the hour it was already down to 2 bar.
2. I then isolated the flow and return of the boiler from the system, released the pressure from the system and performed the test again. I could tell the boiler was isolated as the pressure gauge on the boiler stayed constant at 0 bar whilst the system increased to 3 bar.
Given that the pressure still dropped after isolating the boiler I can conclude (unless my test is not valid) that I have a leak in the system pipework. Now this is really concerning as there is no evidence of a leak and I am scratching my head trying to work out what to do next. I have already added a couple of containers of leak sealer some time ago, but this does not seem to have helped.
I can go around and make sure all of the rad valves are tight, but can anyone comment that my test is valid given I have not fully drained the system. Unless the air I am pumping in is dissolving in the rad water which is causing the air pressure to decrease then I would like to think my test is valid.
Any pointers really appreciated.
Thanks
Our sealed central heating system keeps losing pressure and we have to top it up very frequently. So in an attempt to work out whether it is the pipework at fault or the boiler I have done the following.
1. I connected a pressure gauge to one of the rads and pressurised the system to 3 bar. The 3 bar pressure did not hold and within the hour it was already down to 2 bar.
2. I then isolated the flow and return of the boiler from the system, released the pressure from the system and performed the test again. I could tell the boiler was isolated as the pressure gauge on the boiler stayed constant at 0 bar whilst the system increased to 3 bar.
Given that the pressure still dropped after isolating the boiler I can conclude (unless my test is not valid) that I have a leak in the system pipework. Now this is really concerning as there is no evidence of a leak and I am scratching my head trying to work out what to do next. I have already added a couple of containers of leak sealer some time ago, but this does not seem to have helped.
I can go around and make sure all of the rad valves are tight, but can anyone comment that my test is valid given I have not fully drained the system. Unless the air I am pumping in is dissolving in the rad water which is causing the air pressure to decrease then I would like to think my test is valid.
Any pointers really appreciated.
Thanks